Discuss 3 Fluke testers, different results? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

doogle

-
Reaction score
1
testing an installation(that we have just finished) where the client want to choose a few circuits and check it against the test sheets, Now the circuits are 3- 240mm single core cables in parrallel (24 in total in a data centre) I have tested r1+r2 with 3 different fluke multi function testers that have been callibrated and i get different readings every time,as in 1 tester will give me 2 or 3 different readings on the same circuit , the next 2 or 3 completely different readings and so on,changed batteries, swaped leads, but nothing seems constant, doing my head in,one told me a 6m run had more resistance(0.05 no way) than a 70m run(0.01), only thing i can think of is Edmunsons can't callibrate properly and are ripping us of, think readings should all be about 0.00 -0.01 but getting -0.03 to 0.18( different every time)
 
You're trying to measure quite low values at the limit of the range/resolution of the instruments so any errors from probe contact etc. will appear to be amplified.

+/- 0.2 ohms I wouldn't really lose any sleep over.
 
Thanks for that, Fluke does seem a bit random compared to the meggers we used to use, is there a meter that can measure resistance in micro ohms?
 
As Archy hinted you are expecting precision beyond the capability of your Fluke MFTs. If you wish to measure such values with greater precision you require a special type of micro-ohmeter called a Ductor. Probably best to hire one if you do not have a regular requirement as they are expensive pieces of kit.
 
As Archy hinted you are expecting precision beyond the capability of your Fluke MFTs. If you wish to measure such values with greater precision you require a special type of micro-ohmeter called a Ductor. Probably best to hire one if you do not have a regular requirement as they are expensive pieces of kit.

You also need to know how to use a Ductor tester too, ...ie, test kit settings and testing position of current and potential spikes.... You'll also have to substantially bridge the cables at one end under test, as you don't use wander leads with this kit!! lol!!
 
ive tested for over 6 years with various meters and never come across a high Ze on a TNC-S. Now i've got this fluke 1652C ive found two seperate installations with the tnc-s Ze over 0.68!!!. is it the meter or just a coincidence???
 

Reply to 3 Fluke testers, different results? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock