Some advice please.. I am going to replace a 1361 fusebox, only 5 circuits, with a new consumer unit. However I have noticed that the ring 30A circuit is still energised after I pulled the circuit fuse. Further investigation revealed another 16A cct is connected and only once this fuse is pulled does the circuit go dead. So obviously it must be connected also somewhere. This strikes me as dangerous, not in current carrying capacity (the wires are old colour, stranded, about 3-4mm2 i would say) but to isolate properly.
I did a figure of 8 continuity test on one pair wires and then another pair and it is continuous, so there is a ring. Which pair is the real ring though is unclear, maybe the pair with the highest readings?
If I can't discover where the "extra" leg has been joined, what do you suggest I do? Join all three into the one circuit? If I left one wire out it would still be live..
I did a figure of 8 continuity test on one pair wires and then another pair and it is continuous, so there is a ring. Which pair is the real ring though is unclear, maybe the pair with the highest readings?
If I can't discover where the "extra" leg has been joined, what do you suggest I do? Join all three into the one circuit? If I left one wire out it would still be live..