Discuss 3 phase heater problem in the DIY Electrical Advice area at ElectriciansForums.net
F
Flakey
Hi there,
I have a number of 22kw heater sunning of 3 phase supply. There is a dial with 4 settings 1 being the lowest output 4 the highest.
The problem I have is when ever it is set to maximum output it is knocking out the breakers not discriminating at the rcd but knocking out the main breaker as we'll. When I have opened the unit 1 pf the connections to one of the heating elements has burnt out. It has happened to a couple of other units too.
Could it be it do with the system not being adequately balanced?
Any help would be greatly appreciated.
James
The burned connections are more likely down to poor terminations than balance. The tripping fault could be balance related or it could just be plain old fashioned overload. You're going to need a sparky with some test equipment to establish the circuit loading etc.
Reply to 3 phase heater problem in the DIY Electrical Advice area at ElectriciansForums.net
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Hi, leading on from my question the other day about running the 3 phase compressor off my 8.5kW generator I have since got my hands on a 240v to 3...
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...