Hi all

Its not often i work with 3 phase so am looking for a bit of advise on cable and circuit breaker size. I have a job to install an isolator for a motor extraction in a small spray booth getting installed in a workshop. I was planning on using 2.5mm single core cable in already installed metal trunking with a 6A type c triple pole circuit breaker. The detail i have on it is
500 BDA
[email protected]
1.5kw motor
2640rpm - 2pole
400w 3 phase 50hz
d90s
FLC 3.0A
SC 21A
 
How did you calculate the mcb size and cable size?
What did the manufacturer say when you asked them what supply they recommend?


Sent from my iPad using Tapatalk
 
Cable size is fine for that load. You could go C16 for OCPD if Zs is satisfactory. That fan will spin up quick so start current will be very short. C6 would be fine. Your data states a starting current of 21A with a running current of 3A.
 
  • Like
Reactions: 1 person
wot he said.a dol with overload and use a C16 MCB.
 
  • Like
Reactions: 1 person
Wot they said. ^^^^
If your ZS is ok the C16 will be ok for short circuit and overload protection of the supply. Then stick an isolator near the motor with a suitably rated DOL which comes combined with an overload device which is suitably rated for the motor.
 
Thanks for your replies a will get a c16 breaker, I am only wiring and installing isolator supposedly

If you are only installing the supply then get the person who has designed the supply to give you the information you need.


Sent from my iPad using Tapatalk
 
Don't try to protect the fan with the MCB, protect the circuit with the MCB and use a DOL starter or manual motor starter to protect the motor.
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
3 phase motor
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
mmelectrics,
Last reply from
spary,
Replies
10
Views
2,354

Advert