Hi guys, I'm mainly a housebasher but done a few bigger jobs when serving my time. In past two years I've wired my dads pals car garage. Nothing major just wired an office some extra lights etc also wired 3 3phase car ramps.

Now the problem/question I have is when testing circuits everything was fine also checked phase rotation everything was great. But when actually testing the ramps 2out the 3 ran backwards ( up was down /down was up) when this happens I was always told to rotate the last two phases ( l2/l3) so i done this and ramps worked. Tested the phase rotation and it was showing up 321 instead of 123 on my fluke mft? So obv this would be classed as the phase rotation being reversed? Now I'm abit stumped because as I said my tests showed all rotation going same way and correct etc but yet still ramps ran backwards?

Am I missing something? :sad_smile:
 
You check phase rotation in 3 ph premises to confirm all 3phase mains and submains are sequenced the same, when connecting loads like motors etc its common to find they may be in reverse and where this is the case just swapping any 2 phases at the outgoing of the isolator or incoming of the ramp controls will suffice.

Reverse phase rotation isn't an issue unless different 3ph sockets and dist' boards etc are opposite to each other.... hench plugged in loads will work correctly in some sockets and backwards in other (if phase rotation conscious of course)
 
as above. swap 2 phase round on the ramps, not the supply.
 
Sometimes you can get a phase crossed at the incomer,seen that before but as Darkwood said so long as all the 3 phase sockets are wired the same then don,t worry too much
 
Sorry shoulda made that clearer was just at the ramp I reversed the last two phases not at the db or isolator. Just thought I musta been missing/doing something wrong. Next question to follow on is same garage is getting a 3phase compressor. Just a single phase one there at the moment. I'm planning on using a 3phn&e commando socket and plug. I'm presuming it will have a flex on it (compressor hasn't been ordered yet) is there a chance the compressor will run backwards ? Apart from phase rotation is there any other tests I could do to make sure I've got it going the right way? Don't fancy getting it wrong ! Never wired up a 3phase compressor before lol
 
all depends on how the compressor has been wired. best way is to connect up, switch on, and see which way it runs. reverse it if necessary. ( that is after you've done dead testing to ensure it's safe to energise ). one thing i'd suggest is to make sure the motor is connected in star configuration. if it's dual voltage and you connect it in delta, you'll bugger it.
 
Basically just wire the socket up as normal l1 from supply to l1 in socket same for l2to l2 and l3 to l3 then make sure you get wires right way around on compressor and off you go.You will not do any harm to it if you get it going backwards,again just reverse 2 phases.Incidentally you probably wont need a neutral at the compressor they normally just use 3 phases and earth,hard to say if it will come prewired some do some don,t.
 
Basically just wire the socket up as normal l1 from supply to l1 in socket same for l2to l2 and l3 to l3 then make sure you get wires right way around on compressor and off you go.You will not do any harm to it if you get it going backwards,again just reverse 2 phases.Incidentally you probably wont need a neutral at the compressor they normally just use 3 phases and earth,hard to say if it will come prewired some do some don,t.

this is what I was planning on doing thanks.

thanks for all the replies guys.
:-)
 
suggest you use a 4 core SWA to feed the socket. then if you need a N, you can use the armour as cpc.
 
  • Like
Reactions: 1 person
when carrying out a phase rotation test you need to test for correct sequence at all connections on that circuit......as its easy for..lets say L1 and L2 to cross for a portion the circuit....then revet back to correct sequence at point of use..
 
  • Like
Reactions: 1 person
Id have dug the road up disconnected the supply cable ,turned it around so the cores line up in the correct order when ready for termination.... then sacked the cable team who layed it in backwards :) ... seen this loads times on upgrades when they couldn't physically splice into the main line on the street in the correct sequence.
 
  • Like
Reactions: 2 people
I did the phase rotation at load side of isolator in db then feed side at 20a rotary isolator. Then once ramps had been installed Load side at 20a isolator then again at the ramp. ? Plus the other zs tests etc. if the service head ( which I would call cable head?? Same thing I'm presuming) was round the wrong way I would probably have phoned Scottish power out as its there gear and surely would be there problem to fix? Same as if someone's house cable head had a fault I'd phone them? Had that a few times and once had to full the main fuse cause it was arcing that badly it was melting/charring it. Thot the sp guy woulda been abit dodgy with me pulling it but he said the general consensus was that as long as it was a spark pulling the fuse ( for a reason, fault/new tails etc) and aslong as the meter was still sealed (apart from the connections) they didn't care? Anyway side tracking abit here. Lol
 
I almost did that when i was doing an EICR for two adjacent factories owned by same Company as one supply was 123, the other 321. Then i counted up how many TP circuits there were and how many DBs and thought bloody hell that will take some sorting, not to mention the downtime. Sod that !
Anyway, ended up marking all the boards as phase 321 so the next poor sod who tries to connect up a machine the right way round has a chance.
It was funny as they were a little down on the previous spark for always connecting up the machines backwards. He was clearly just following the colours - bless.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3phase question
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
paul_h,
Last reply from
plugsandsparks,
Replies
17
Views
1,906

Advert