Hi I come across this once in while. When performing a zs non trip test on at 6amp mcb. It trips out. It's always on the cheaper boards. I've read on other sites that it is because of cheap Chinese mcbs. I havn't come across the topic on here and was wonder what you guys thought?
 
Hi Mike, This can happen on any low current rated MCB, irrespective of manufacturer or origin. In this situation the easiest solution is to calculate Zs by adding your Ze and R1+R2 together. Alternatively you could temporarily replace the MCB with a higher value and measure Zs, but this is considered bad electrical practice because you would be testing with different fault protection in place.
 
Just a thought,

Can you use the method someone on here mentioned the other day, (sorry I forgot who posted it), where you open the MCB (first) and then you join L+CPC at the far end, and measure across the MCB ?

Apologies to whoever posted this originally
 
Last edited by a moderator:
Hi Mike, This can happen on any low current rated MCB, irrespective of manufacturer or origin. In this situation the easiest solution is to calculate Zs by adding your Ze and R1+R2 together. Alternatively you could temporarily replace the MCB with a higher value and measure Zs, but this is considered bad electrical practice because you would be testing with different fault protection in place.

Yeah that's exactly what I did! Thanks. I thought it was just interesting and wondered why it was happening. Is it an indication of a faulty mcb? Or is it a bit sensitive.
 
megger 1552 used to trip alltime when testing 6a used to just temp move up to higher rated breaker, but switched to megger 1553 and problem seems to of gone away
 
Just do the test on a 'no trip' test. The reason the MCB sometimes trips when you carry out the high current loop test is because you are putting 25A through the installation. I don't understand exactly how the whole test works but somehow they use a much lower applied current of 15mA to do the no trip test hence why the MCB doesn't even cough. Just have a look at the data sheet for the 1500 series Meggers to see what i mean (LINK).
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
6amp mcb tripping on non trip Zs test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Mike Me Mate,
Last reply from
ezzzekiel,
Replies
6
Views
3,941

Advert