Struck me recently as to why we use 6mm T&E for a 32A cooker circuit, when generally 4mm (clipped direct) would be sufficient. Is this a historical thing with BS3036 fuses?
 

i=p/u

Electrician's Arms
Messages
6,847
Location
n.ireland/ Scotland
37A clipped direct then consider fuse factor....

its like myn tutor told me, if you want to win jobs, then do the calcs and know your stuff , where everyone just throws in 6mm
 