A
alasdairp
Thanks for responding.
However:
599 just allows "flexible cable" and has nothing about the cable rating. The drop flex is clearly visible - effectively an appliance lead wired to the rose instead of plugged - so is not really a part of the "main wiring installation". It may be replaced by a non-electrician.
433.1.1 states that the ocpd must be rated no more than 1.45 times the rating of the lowest cable (here 6A for 0.75mm2 cable) so MCB needs to be less than 8.9A - hence it has to be a 6A one - to meet the Regulations.
So, I still believe that my interpretation is correct.
However:
599 just allows "flexible cable" and has nothing about the cable rating. The drop flex is clearly visible - effectively an appliance lead wired to the rose instead of plugged - so is not really a part of the "main wiring installation". It may be replaced by a non-electrician.
433.1.1 states that the ocpd must be rated no more than 1.45 times the rating of the lowest cable (here 6A for 0.75mm2 cable) so MCB needs to be less than 8.9A - hence it has to be a 6A one - to meet the Regulations.
So, I still believe that my interpretation is correct.