Hi,
You can probably get a copy of the above standard at your local library, whilst you are about it have a read of
[h=1]BS 2754:1976+A1:1977 I know it has been withdrawn but it will give you a bit of a education. Now you need to remember what the bonding wire is for, it is to keep the touch voltage down to a reasonable value and cause the supply fuse to blow in a reasonably short time without being subject to physical damage. It is likley that the supply fuse to these units will be a BS 1362 fuse link and that the power supply it self will have double insulation between the mains supply and any selv (32V or less) supply within the unit. [/h]
These units should have been subject to type testing where first off the production line and and randomly there after are subject to severe testing on the earth bond and the double insulation.
In the case of the earth bond, it is typicaly required in this type of instance to be tested at 25A for 60 seconds and maintain a resistance of less than 0.1 ohm throughout the test and not subject to damage from over heating. Likewise the double insulation will be tested to twice the normal flash test voltages for 60 seconds and have no sign of breakdown. Due to the nature of the type testing flash test the unit is not considered safe for further use and must be destroyed.

Given the use of the safety earth conductor, which is protected within the appliance then 1mm may be more than adequate.
 
Hi Midwest,

I know what you're saying and it worries me, hence asking for advice on here. The problem I run into is that there doesn't appear to be a BS for the products we make. There is a document on the government website that is very informative but just states that the equipment has to be safe, without any specifics. I sometimes struggle with the vagueness of the information provided, including BS 7671. Its statements like a "where reasonably practical" etc. Just tell me to use a 2.5mm cable!

Raparee thanks for for that article and your help. Not sure if we'd be able to flash test our units without destroying them as some of the components are a little bit temperamental at the best of times but I want to make sure we carry out the other tests on every peice of equipment that leaves the building. It's helped comparing notes.

Rich

You may find that the routine flash test is "normative" in the standard, this means you will do this unless you have got a very very good technical reason why not, and components being temperamental is not an excuse. I have seen the inside of one of these parking machines and it doesn't seem if that one was designed with static protection and other issues in mind! The unit should have been certified as safe by an external test house and should be able to advise on routine testing. If you need more help contact York EMC at Yate.
 

Reply to Advice needed with manufacturing electrical equipment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, I am new to photovoltaic system installation, can you guys give me some advice. Currently I plan to purchase a Maysun Solar 800W...
Replies
0
Views
729
Hi all, Figured I'd come straight to the experts with this one because I don't have a great deal of electrical experience. I'm a designer at a...
Replies
21
Views
2K
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
538
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
212
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock