Hi, I have an issue I cannot get my head round.

I have been asked to replace a consumer unit, and the circuits are run in steel conduit with singles for live and neutral and using the conduit as the earth for sockets and lighting. There is also an MICC cable supplying the cooker.

There are two conduit’s entering from the bottom of the CU, and one conduit from the top of the CU along with the MICC entry.

My problem is modern consumer units are taller than the old ones, and I don’t know if it is practice to cut and rethread steel conduit fixed in place and containing cables.

I would consider mounting the new consumer unit in front of the existing unit so the conduit and MICC does not need to be disturbed, but my worry is that once the new consumer unit is in place, the earthing for all circuits is only accessible by dismantling the current consumer unit.

Any Advice?

Regards
Ps Sorry about repeated images, but there is no way to remove an image if added by mistake and no way to reset the add new thread that I can find.

IMG_7118.JPG


IMG_7119.JPG


IMG_7118.JPG


IMG_7119.JPG


IMG_7118.JPG


IMG_7118.JPG


IMG_7118.JPG


IMG_7118.JPG
 
as a suggestion, you could cut the existing CU casing down to about 35mm , leaving the existin back half with the conduits in it as a pattress to screw the new CU on top of. extend the cables with wagos. i'd recommend sa thourough testing esp. of the conduit as cpc.
 
as a suggestion, you could cut the existing CU casing down to about 35mm , leaving the existin back half with the conduits in it as a pattress to screw the new CU on top of. extend the cables with wagos. i'd recommend sa thourough testing esp. of the conduit as cpc.


Thank you,
Sounds like a plan although there is still the problem that the actual earthing connections are inaccessible being inside the pattress section.
 
strap a fly lead from the pattress to the new CU case and to the earth bar.
 
No chance of getting one or two adaptable boxes in there ? Mind you I probably would not want to be undoing that MI gland. They look imperial those conduits, could improve it by fitting serrated washers.
 
No chance of getting one or two adaptable boxes in there ? Mind you I probably would not want to be undoing that MI gland. They look imperial those conduits, could improve it by fitting serrated washers.

I had not even though about imperial fittings. I will defiantly be leaving the existing connections in place. My current though is to use self tapping screws to attach the new CU over the front of the existing CU and supporting it if required.
 
I have seen new boards fitted over old but the existing board is often flush. I would only fit over old one as a last resort, mainly because even though it will be safe it will look terrible.
 
I had not even though about imperial fittings. I will defiantly be leaving the existing connections in place. My current though is to use self tapping screws to attach the new CU over the front of the existing CU and supporting it if required.
That is not a bad idea, all cable entry's in the back, fly lead an earth from old to new. Shame there is no room at the side.
 
Last edited:
Hi, I have an issue I cannot get my head round.

I have been asked to replace a consumer unit, and the circuits are run in steel conduit with singles for live and neutral and using the conduit as the earth for sockets and lighting. There is also an MICC cable supplying the cooker.

There are two conduit’s entering from the bottom of the CU, and one conduit from the top of the CU along with the MICC entry.

My problem is modern consumer units are taller than the old ones, and I don’t know if it is practice to cut and rethread steel conduit fixed in place and containing cables.

I would consider mounting the new consumer unit in front of the existing unit so the conduit and MICC does not need to be disturbed, but my worry is that once the new consumer unit is in place, the earthing for all circuits is only accessible by dismantling the current consumer unit.

Any Advice?

Regards
Ps Sorry about repeated images, but there is no way to remove an image if added by mistake and no way to reset the add new thread that I can find.

View attachment 34021

View attachment 34022

View attachment 34023

View attachment 34024

View attachment 34025

View attachment 34026

View attachment 34027

View attachment 34028
Hi, I have an issue I cannot get my head round.

I have been asked to replace a consumer unit, and the circuits are run in steel conduit with singles for live and neutral and using the conduit as the earth for sockets and lighting. There is also an MICC cable supplying the cooker.

There are two conduit’s entering from the bottom of the CU, and one conduit from the top of the CU along with the MICC entry.

My problem is modern consumer units are taller than the old ones, and I don’t know if it is practice to cut and rethread steel conduit fixed in place and containing cables.

I would consider mounting the new consumer unit in front of the existing unit so the conduit and MICC does not need to be disturbed, but my worry is that once the new consumer unit is in place, the earthing for all circuits is only accessible by dismantling the current consumer unit.

Any Advice?

Regards
Ps Sorry about repeated images, but there is no way to remove an image if added by mistake and no way to reset the add new thread that I can find.

View attachment 34021

View attachment 34022

View attachment 34023

View attachment 34024

View attachment 34025

View attachment 34026

View attachment 34027

View attachment 34028
 
Yeah I keep looking at them, Im not sure.
I am certain, the MI is if you look at the sleeving. One of the bottom entry conduits appears to be terminated at an oversized entry. They also have lockouts locking the conduit to the couplers, that is definitely a method I haven't seen for years. State of those conduits though I would think a rewire is probably in order.
 
I am certain, the MI is if you look at the sleeving. One of the bottom entry conduits appears to be terminated at an oversized entry. They also have lockouts locking the conduit to the couplers, that is definitely a method I haven't seen for years. State of those conduits though I would think a rewire is probably in order.
Yes those lock nuts do give a clue.
 
If I was asked to quote for that, I would put a very high price in ...... so that some other mug does it.

I was the other mug. A little old lady that has been told by her sister that it looks dangerous and so she insists it is changed.

I tried an EICR hoping to be able to convince the lady that the installation is not significantly more dangerous than when installed, but found problems that mean I must recommend a CU change, although I actually believe it would be better to make a few minor repairs and not change the consumer unit.
 
I was the other mug. A little old lady that has been told by her sister that it looks dangerous and so she insists it is changed.

I tried an EICR hoping to be able to convince the lady that the installation is not significantly more dangerous than when installed, but found problems that mean I must recommend a CU change, although I actually believe it would be better to make a few minor repairs and not change the consumer unit.
What problems to suggest a CU change.
 

Reply to Advice on consumer unit replacement. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
I live in a flat in Scotland supplied with an old 2 meter system called THTC where one meter using a time signal supplied heating and hot water...
Replies
7
Views
1K
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
852
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock