Discuss Anyone can fix an MICC cable leading to a light switch in my house (London, N6)? in the UK Electrical Forum area at ElectriciansForums.net

D

Deleted member 148954

Hello, I am looking for an electrician who has an expertise in dealing with MICC (mineral-insulated copper-clad) cables. It is a domestic job in my house (I live in Highgate, London; postcode is N6). When I was replacing a light switch in my living room, 2 out of 6 wires coming out of 2 MICC cables (which come through the wall; each cable has 3 wires) broke off. I am attaching two photos of the light switch in question (the 2 wires that have snapped are behind the switch). Please contact me if you can do the job and provide a quote. (If you need any further info, please let me know). Thanks, Eugene
 

Attachments

  • 20220908_115231.jpg
    344.5 KB · Views: 146
  • 20220908_115315.jpg
    424.3 KB · Views: 136
Not sure if any member is close to you, but we will soon find out.

MICC is a fairly specialist area now. Not used so much nowadays as a new install.
If the core snapped right at the pot (I still know the lingo!) it’s going to need replaced.

Looks like it’s buried in plaster on a brick wall.

What do the switches control? If they’re all in the same room, likely solution is to have only one switch, controlling all lights and taking that length of cable out of circuit.
Or remake the end of both cables, bringing the switch up the wall a bit.
Or remake the cables high up on the wall, fitting in a box to use as a joint box with a blank plate… then extend in regular t&e cable back down to switch.


Have never know MICC to be used domestically except as a sub main up a tenement building in Edinburgh.
Was my brothers flat, and all the sub mains were bare copper MICC clipped surface up the stairwell. Amazing neat job.


Edit. Just saw Dusty’s reply….. Is that the celeb spark, Delroy? Love to see him work on MICC on YouTube… lol
 
There are a few old house round my way where where MICC was buried just like that in the render and runs here there and everywhere exactly like above with it potted into a back box

More often than not it doesn't follow any safe zone so can be a bit of a pig to work in these houses and I have found the MICC running diagonal much of the time
 
More often than not it doesn't follow any safe zone so can be a bit of a pig to work in these houses and I have found the MICC running diagonal much of the time
I thought MICC complies with 522.6.204, so hadn't previously thought that diagonal running is actually an issue?
 
I thought MICC complies with 522.6.204, so hadn't previously thought that diagonal running is actually an issue?
It may have complied back in the day but still a nightmare if you are drilling 6mm holes to put up a shelf or TV bracket and drill straight through the buried MICC
 
Not sure if any member is close to you, but we will soon find out.

MICC is a fairly specialist area now. Not used so much nowadays as a new install.
If the core snapped right at the pot (I still know the lingo!) it’s going to need replaced.

Looks like it’s buried in plaster on a brick wall.

What do the switches control? If they’re all in the same room, likely solution is to have only one switch, controlling all lights and taking that length of cable out of circuit.
Or remake the end of both cables, bringing the switch up the wall a bit.
Or remake the cables high up on the wall, fitting in a box to use as a joint box with a blank plate… then extend in regular t&e cable back down to switch.


Have never know MICC to be used domestically except as a sub main up a tenement building in Edinburgh.
Was my brothers flat, and all the sub mains were bare copper MICC clipped surface up the stairwell. Amazing neat job.
Seen loads of domestic pyro in the past.
As regards the photo, it looks like the cables are going through the wall, (OP mentions it) at the mortar seam. There isn't enough length, at present, to remake off the pyro ends so it all depends on the other side of the wall and making available enough to work on.
Cable trace to start with.
 
a good old fashion spark would sort the out if he has the tools, I bet some young uns never done anything like that, it will blow the brains out looking at never mine playing with it, hands up if you done work like that, still got me old tools.you will never know when you need them.
 
a good old fashion spark would sort the out if he has the tools, I bet some young uns never done anything like that, it will blow the brains out looking at never mine playing with it, hands up if you done work like that, still got me old tools.you will never know when you need them.

I've done it and still do it, both repairs/rework of old cable and installation of new.
 
My dad has all his old pyro tools in a wooden box in his garage , it can say neither of us have used it in probably 5 years or more

he has some lovelty old junk , like wooden handle files , some really old eclipse hacksaws all from when he did his apprenticeship back in the mid 1950s
 
Hello, I am looking for an electrician who has an expertise in dealing with MICC (mineral-insulated copper-clad) cables. It is a domestic job in my house (I live in Highgate, London; postcode is N6). When I was replacing a light switch in my living room, 2 out of 6 wires coming out of 2 MICC cables (which come through the wall; each cable has 3 wires) broke off. I am attaching two photos of the light switch in question (the 2 wires that have snapped are behind the switch). Please contact me if you can do the job and provide a quote. (If you need any further info, please let me know). Thanks, Eugene

Can you post a picture of what's left inside the switch?

Is there any writing on the black insulation of the conductors inside the switch? Hopefully it will have the cable size written on it to help identify what size fittings will be required for repairing it.

A lot of the flush MICC installs I've come across/dealt with have been imperial sized cables which can add another little bit of complexity to the situation.
 
a good old fashion spark would sort the out if he has the tools, I bet some young uns never done anything like that, it will blow the brains out looking at never mine playing with it, hands up if you done work like that, still got me old tools.
Mine are in the van.
A couple of years since last used.

Got a church Test and Inspection soon, done in pyro.
 
A lot of the flush MICC installs I've come across/dealt with have been imperial sized cables which can add another little bit of complexity to the situation.

Agreed, the cables looks large relative to the seals. Are they 5/8" seals on 0.0015 sq ins. cable? Hopefully an inside view of the seals and sleeves will resolve that question. Although I expect the OP is simply looking for a contractor to do the work, rather than chat about it on here, eliciting any complications might help the said contractor prepare for the job and not arrive without the necessary bits.

It looks like there is just about enough cable there to make the ends off again and have an inch beyond the disc to put a Wago on. But has anybody ever jointed a conductor within a pot and sealed it up again? I think one would have to be very careful to avoid soldering flux wicking into the insulant and deflux thoroughly before filling with compound. But it might be possible, especially if one is prepared to go to the trouble of making a scarf joint in the conductor. Then again, not much room in a 5/8" seal if that is what they are.

I wonder how they came to break in the first place? Perhaps the conductors were nicked with the stripping tool and weakened. It would take a lot of mauling to break an otherwise completely intact conductor.
 
Thanks for your reply. I'll contact you shortly.
Not sure if any member is close to you, but we will soon find out.

MICC is a fairly specialist area now. Not used so much nowadays as a new install.
If the core snapped right at the pot (I still know the lingo!) it’s going to need replaced.

Looks like it’s buried in plaster on a brick wall.

What do the switches control? If they’re all in the same room, likely solution is to have only one switch, controlling all lights and taking that length of cable out of circuit.
Or remake the end of both cables, bringing the switch up the wall a bit.
Or remake the cables high up on the wall, fitting in a box to use as a joint box with a blank plate… then extend in regular t&e cable back down to switch.


Have never know MICC to be used domestically except as a sub main up a tenement building in Edinburgh.
Was my brothers flat, and all the sub mains were bare copper MICC clipped surface up the stairwell. Amazing neat job.


Edit. Just saw Dusty’s reply….. Is that the celeb spark, Delroy? Love to see him work on MICC on YouTube… lol
Thanks for your reply. Very helpful input.
 
Can you post a picture of what's left inside the switch?

Is there any writing on the black insulation of the conductors inside the switch? Hopefully it will have the cable size written on it to help identify what size fittings will be required for repairing it.

A lot of the flush MICC installs I've come across/dealt with have been imperial sized cables which can add another little bit of complexity to the situation.
Thank you for your reply. There is no writing of any kind on the black insulation of the conductors. I'll post a picture of what's left inside the switch tomorrow morning. In the meantime, here are the pictures of the conductors that have snapped. Are these the imperial size in your estimation (don't know if it is possible to determine from the pictures). Thanks.
 

Attachments

  • 20220912_184655.jpg
    407.4 KB · Views: 114
  • 20220912_185114.jpg
    329.8 KB · Views: 108
looks like there is just about enough cable there to make the ends off again and have an inch beyond the disc to put a Wago on. But has anybody ever jointed a conductor within a pot and sealed it up again? I think one would have to be very careful to avoid soldering flux wicking into the insulant and deflux thoroughly before filling with compound.

That's exactly what I was thinking when I asked for a pic inside the switch. dig the old compound out, solder some extensions on and re-seal. I'd be game for giving it a go if I had time.
It would take a lot of mauling to break an otherwise completely intact conductor.

I don't know what the size is but the smallest imperial size MICC I've worked with is pretty tiny and easily snappable
 
But has anybody ever jointed a conductor within a pot and sealed it up again? I think one would have to be very careful to avoid soldering flux wicking into the insulant and deflux thoroughly before filling with compound. But it might be possible, especially if one is prepared to go to the trouble of making a scarf joint in the conductor. Then again, not much room in a 5/8" seal if that is what they are.
Yes I have, I just took my time. Prepared the ends of the conductors with a needle file, the scarf was not much of an angle, and I'm sure if I did it again I'd get away with a butt joint as described in the handbook. I was also able to remove the pot for better access. The cable was coming down the wall so that helped with keeping flux away, I did also use a flux cleaner, mostly to prevent the flux causing future corrosion. I used a fairly powerful micro jet type torch to silver solder the joint and a small oxy/mapp torch to preheat the end of the cable to prevent it sinking all the heat away, roughly following the Pyrotenax cable handbook instructions for jointing cable ends. I also used one of those helping hands things to hold the ends during soldering, I was able to fix that to the wall using one of the switch box wall fixing holes. The repaired cable passed the insulation tests off the scale of the meter. I did unclip a fair section of the cable from the wood panelling to prevent the risk of hot cable burning the wood.

The main reason for repairing rather than replacing was because I got to use a blowtorch the bare cable was very neatly run with 2 others from the same switch, the cable run was very visible so a joint box wouldn't look good and accessing the other half of the cable for replacement would be impractical as it would damage the ornate plaster covings etc.

I'm not sure why the conductor broke, was called out because the light was flickering and when the switch was unscrewed from the backbox the conductor pulled out of the sleeve, broken at the tip of the stub cap. No sign of damage or corrosion, must have been weakened during installation. I did have the benefit of this cable being metric though so it was easy to find a replacement pot. I'm not too good at opening old pots carefully to be able to reclose them. The pot was fitted a little past the gland too so I could remove a bit of the sheath for a tight fit for the new pot.

Not a quick job, I don't get many chances to improve my skills with this sort of work to be able to do it faster. I wish I'd taken some photos.
 
the scarf was not much of an angle, and I'm sure if I did it again I'd get away with a butt joint as described in the handbook. I was also able to remove the pot for better access. The cable was coming down the wall so that helped with keeping flux away, I did also use a flux cleaner, mostly to prevent the flux causing future corrosion. I used a fairly powerful micro jet type torch to silver solder the joint and a small oxy/mapp torch to preheat the end of the cable to prevent it sinking all the heat away,

I was thinking that a plain scarf would be best silver-soldered, but a soft-soldered joint might be equally satisfactory if bound with some 32SWG TC wire first. I'd probably want to support the conductor to file it, e.g. drill the right diameter hole in a small block of material e.g. hardwood and cut the angle on one end. Feed the conductor through the hole and file it flush with the block. If it had to be done in situ in the pot, one could do something similar with a little piece of tubing.

Perhaps one of those mini spot-welders for putting the inter-cell links on battery packs would make a good weld of this size? Would avoid the flux issues and make a very quick job of it.

Many decades ago, one of my mentors did some very crafty jointing to the leadouts of a valuable prewar CRT that had been in someone's garden for years and the leads had corroded off at the welds. There were tiny, weak stubs remaining in the pinch but he managed to get inside with some 26SWG and make successful joints, and the tube turned out to be a corker.

There is no writing of any kind on the black insulation of the conductors.

The fact that it is not emblazoned with 'STUB SLV' etc. hints at it being imperial
 
I also wondered at first whether there were dings in it, but now I'm more inclined to think it's an artefact of the pic.
 
That's exactly what I was thinking when I asked for a pic inside the switch. dig the old compound out, solder some extensions on and re-seal. I'd be game for giving it a go if I had time.


I don't know what the size is but the smallest imperial size MICC I've worked with is pretty tiny and easily snappable
Here are the pics of what's behind this switch. Hopefully they help figure out what could be done here. Thanks again for your help.
 

Attachments

  • 20220913_102225.jpg
    431.2 KB · Views: 92
  • 20220913_102315.jpg
    371.2 KB · Views: 85
  • 20220913_102330.jpg
    392.2 KB · Views: 81
  • 20220913_102431.jpg
    385.7 KB · Views: 82
  • 20220913_102526.jpg
    355.8 KB · Views: 91
It's a pity we can't see the seal discs clearly or exactly where within them the conductors have snapped. But scaling the size off the pic compared to the box and cable, I am increasingly convinced that they are 5/8" seals on imperial cable. If the existing seals can't be salvaged and re-used, metric pots can be fitted; it may be necessary to drill out the cable entry and solder to the sheath, according to the specific cable diameter.

@Eugene: Do you know what year the property was built / wired? Is the circuit protected by an RCD or RCBO? Could you tolerate the box being moved 5cm up the wall?

Slightly odd setup there, with two cores from one cable and one from the other going to each gang of the dimmer, but there are a number of reasons why that might have come about. Clearly some previous convictions with those bits of terminal block.
 
It's a pity we can't see the seal discs clearly or exactly where within them the conductors have snapped. But scaling the size off the pic compared to the box and cable, I am increasingly convinced that they are 5/8" seals on imperial cable. If the existing seals can't be salvaged and re-used, metric pots can be fitted; it may be necessary to drill out the cable entry and solder to the sheath, according to the specific cable diameter.

@Eugene: Do you know what year the property was built / wired? Is the circuit protected by an RCD or RCBO? Could you tolerate the box being moved 5cm up the wall?

Slightly odd setup there, with two cores from one cable and one from the other going to each gang of the dimmer, but there are a number of reasons why that might have come about. Clearly some previous convictions with those bits of terminal block.
Thanks. The house was built sometime in the 1960s. Don't know about RCD or RCBO - there is a fuse box of course but that's all I know. Yes, the box can be moved 5cm up the wall.
 
Have never know MICC to be used domestically except as a sub main up a tenement building in Edinburgh.
Sometime around the I think late 50's / early 60's BICC produced the Octpus wiring system which was used for wiring flats I believe it had a central box and all the cables were terminated into it this was laid out on the shuttering and the cables laid out to there various positions before the concrete was poured. A friend of my mum worked at the BICC factory in Prescot terminating the ends on piece work and was paid something like 3d per end it doesn't sound a lot but they could terminate upto 20 ends per hour. I remember seeing the film at college back in the 70's and it was amazing how they did it

Around Prescot you quite often find the odd older house wired in MICC usually the owner or past owner worked at the MICC part of the factory or were a relative of someone who worked there
 
I
Sometime around the I think late 50's / early 60's BICC produced the Octpus wiring system which was used for wiring flats I believe it had a central box and all the cables were terminated into it this was laid out on the shuttering and the cables laid out to there various positions before the concrete was poured. A friend of my mum worked at the BICC factory in Prescot terminating the ends on piece work and was paid something like 3d per end it doesn't sound a lot but they could terminate upto 20 ends per hour. I remember seeing the film at college back in the 70's and it was amazing how they did it
A penny a minute, 5 bob an hour, eh?
Must have been in the fifties UNG, maybe early 60’s, though.
I remember the octopus, they used loads in 60’s high rise flats.
 
Why the insulated lugs with metal screws in the switch back box?

It's still not clear to me where, exactly, the wires have broken.
 
Never liked this type of MICC clamp switch box, they were always shallow not designed for dimmers etc.
The better way would of been to use full terminations Micc glands then pot and coupler and bush into a standard deeper box .
 
Last edited:
Never liked this type of MICC clamp switch box, they were always shallow not designed for dimmers etc.
The better way would of been to use full terminations Micc glands then pot and coupler and bush into a standard deeper box .
I agree.... but when that one was designed the best description of a household dimmer was a lamp getting towards the end of it's life.😉
 
I am certain that Del used on of those pancake pyro boxes on a job when he had to repair a damage pyro cable is a garage
 
I am certain that Del used on of those pancake pyro boxes on a job when he had to repair a damage pyro cable is a garage
Yup he did, dont know why he didnt use full terminations into a conduit through box or AB.
Looks the bees when using PVC coated orange and shroud if you please. lol
Maybe Del could not source gland.
 
Last edited:
Nah would look better with a glanded MICC and stop end box , more expensive but a quality job lol
I have always thought those boxes made it look like a cheap job and wasted the effort exerted installing the cable, it's a bit more of a complete job when MICC is glanded looks more reassuring
Orange pvc coated MICC…. Now that’s a proper job!

Fire alarms in red as well?
When it was manufactured in Prescot you could get MICC with any colour serving you wanted if you were prepared to order the minimum quantity which was if I remember 3000m

When BICC manufactured MICC in Prescot they would even supply imperial sized glands and seals which were metric sizes drilled to imperial size
 
I just remember years ago, it think it was going to be a museum or something... general power in orange, fire alarms in red and i think emergency lighting in white.

Apprentices jobs were to stand at the board and basically strip 2-3 foot off each cable as it came into the plant room.
Every day for a week coming home looking like Casper the flippin' ghost!


I think last time i even touched pyro was running a non-stop 500m length through the bowels of Ninewells hospital in Dundee.

There were more corridors under the hospital than appear above ground...

Spooky place sometimes.
 
I have only ever worked with bare and orange pyro

But I am certain I have seen white , grey and red pyro

I still remember clear as day being at a church we were adding some emergency lights and I came across pyro for the first time ( other than at college ) and my heart sank when I had to work on the old pyro circuit , but after a couple hours it wasn't too bad
 
As @UNG says BICC would produce it in any colour provided the quantity was cost effective.
I was also told 'Megger' every gland you make off. Strangely enough was in one of our local churches yesterday and whilst my girlfriend was signing the Queens condolence book I was scratching the MI cables to the light switch thinking they were painted grey but the sheath and shrouds were indeed grey.
 
As @UNG says BICC would produce it in any colour provided the quantity was cost effective.
I was also told 'Megger' every gland you make off. Strangely enough was in one of our local churches yesterday and whilst my girlfriend was signing the Queens condolence book I was scratching the MI cables to the light switch thinking they were painted grey but the sheath and shrouds were indeed grey.
Yup every pot you make off, I always IR the whole coil before installing so I knew it was ok.
Flag out your L with tape after both ends have been IR tested.
 
I think last time i even touched pyro was running a non-stop 500m length through the bowels of Ninewells hospital in Dundee.
Can't remember the last time I used pyro but I can remember one of the first times as a relatively new apprentice when an electrician and myself had to pull a 7L1.5 fire alarm panel repeater link across one of the Pilkington sites through the maze of underground ducts and cellars the run was about 850m and took us the best part of week to do
 
Used to love the micc. Well still do but it is a rare beast today. As above test every end as you go. For surface stuff better looking at it than looking for it - Aka leave a good foot when you run micc in if you are doing a large job and wont make the end off anytime soon.
Anyone who tells you that they have never had an end down is simply a liar.
Pro tip lol check each coil quick ir test before running in 100 mtrs of the stuff.....A lot of time surfaced clipped on the add occasion that you come across a internally twisted coil...i have seen this maybe 10 times in 35 years.
The last english heritage sites I worked on (Roehampton) was ALL surface clipped bare micc probably 20 years ago, Don't know if it is the same now but back then EH insisted that all there properties were wired in micc
Finally Micc > FP anything.
 
Funnily enough I only installed some micc last month, wired staircase lighting in a church tower using white pvc coated and ripped out some rough installed orange coated.
 

Attachments

  • 2F5E04B2-5985-48A9-B000-C8B7C6EA4F1B.jpeg
    759.9 KB · Views: 37
  • 0AE995F2-2981-440A-8323-054D30100D0F.jpeg
    516.4 KB · Views: 36
  • 099B29EC-D494-462B-894F-BC2AAEDB5E04.jpeg
    918.7 KB · Views: 37
  • DC9941ED-1518-42C4-B639-38AB668FE9C5.jpeg
    497.5 KB · Views: 41
  • F4C36FE1-5C0C-42AE-924E-3957D791067A.jpeg
    471.6 KB · Views: 40
  • E07D5492-1A63-4B41-9F7D-B14E04F5E2DE.jpeg
    794.5 KB · Views: 40
  • AFBA0AE7-1C84-4AAC-B6C8-50F6147C8F7C.jpeg
    747.5 KB · Views: 35

Reply to Anyone can fix an MICC cable leading to a light switch in my house (London, N6)? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
Replies
3
Views
623
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
901
Hi all, I posted here some time ago asking for validation of a quote I received for a rewire. (10k assumed 60 points) And got some good advice so...
Replies
2
Views
595
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
487
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock