Discuss Are surge protection devices fitted before or after the main switch in the UK Electrical Forum area at ElectriciansForums.net
Clearly 'tis the season to be grumpy!
How about you guys take a look at his profile and maybe go a little easier on him... it clearly states he's a trainee... just because someone doesn't have the trainee tag, doesn't mean they aren't.
@L1Jay1 , maybe consider signing up for the trainee section of the forums. You'll get a trainee tag so everyone can see you're training and you'll get access to a trainee only area which only trainees, staff and mentors can access so you can ask questions such as this without getting this kind of response.
To answer your question, they would generally be installed after the main switch. The ones in most domestic boards are installed as close to the main switch as possible, many are supplied via a circuit breaker (I've seen 32A for all the ones I've seen) but some, Hager I think, are connected straight to the main switch itself. But as @Strima says... what do the manufacturers instructions say?
Have a think about what the main switch does, and what it is for.
if you don’t know the answer, then maybe someone competent should be doing the work.
I’m simply asking the question
[automerge]1577085576[/automerge]
In the live boards the spd is before the main switch
[automerge]1577085641[/automerge]
What about putting it in the closet ?
What about putting you in the closet
Hi - normally the main switch isolates all the equipment in the board, is that what you mean? :)
Sorry I meant a LVE board , I’ve seen a LVE board with surge protection already installed in it , the SPD is before the main switch in this board , this got me confused.
[automerge]1577089291[/automerge]
Sorry I meant LVE board , not live
This picture illustrates @DPG 's point perfectly. Physically it appears before if you're looking from right to left, but wiring wise it's most definitely after the main switch.
I was trying to think of a way of wording that @DPG, stupid hangover! ?
When you say the SPD is before the main switch, do you mean physical position or actual wiring order though?
in LVE , SPD is before main switch
[automerge]1577093974[/automerge]
In the LVE board it’s before main switch, I’m trying to understand this and the way it’s wired, it appears to be wired before the main switch aswell.
in LVE , SPD is before main switch View attachment 54817
In the LVE board it’s before main switch, I’m trying to understand this and the way it’s wired, it appears to be wired before the main switch aswell.View attachment 54818
In that style of board the SPD is after the main switch. The meter tails terminate into the top of the main switch.
Ideally on an installation all consumer equipment should be after a main switch to allow for safe isolation. But if the supply was split before the main switch then the SPD would have to be before the switch as it is designed to protect the installation and not just the board..
With a lot of manufacturers if the main installation supply fuse (DNO) is below a certain rating there's no requirement for over-current protection for the SPD.
Refering to your LVE board , The incomming tails would terminate into the top of the main switch, so the SPD would be after the main switch.
Sorry I’ve looking at this in the wrong way , the SPD is after the main switch and is pre wired , no need for over current protection , think I’ve got that now
[automerge]1577099221[/automerge]
When SPD is after main switch and is pre wired , then the is no current flowing through it , am I correct .
Whether it needs over current protection is down to the manufacturer.
SPDs are typically metal oxide varistors... At mains voltage these are high resistance and consequently pass no to little current. As the voltage increases, there resistance drops and they conduct more current, dumping the spikes to earth. They may also has discharge arrestors (I think that's what they are called).
The same technology is present in surge arresting extensions which can cause low insulation resistance readings (tip... If an IR test is poor at 500v, if it's good at 250v, it's possibly a surge arrester in circuit).
In normal circumstances there is no current flowing through them. They only become active if transient voltages occur diverting them to earth before it can cause possible damage to equipment. In your pic an earth is required from the device to the consumer unit earth terminal.
Ian 1981 is correct, the devices are after the outgoing terminals of the main switch, in parallel with the busbar. You can see the neutral looped from the outgoing terminal.
I think the correct way is to fit a SPD after the suppliers switch and before the DB isolator, well that is the way all of them are fitted in France, an MCB is required according to the type of SPD, some have overload protection build in.
Reply to Are surge protection devices fitted before or after the main switch in the UK Electrical Forum area at ElectriciansForums.net
Recently I have installed Type 2 Surge Protective Device SPD 20 to 40kA, Type1+2, Phase + Neutral + Earth (2 Pole 275 Volt AC) (Uc-275VAC...
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Wallbox Fuse Box Lite Single Phase has anyone used one of these? I've installed one feeding a Pulsar Max, the Pulsar Max is set to 32Amp max. The...
Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...