I carried out an install on a kitchen in a village hall a while ago I installed some deep back boxes on the brick wall but the builders then installed batons the wall and used insulation board so even my deep boxes weren't close to flush with the wall, I put in some long screws to get round it and went on my way.

They've recently had a sparky come round and tear the place to pieces on an EICR and he's come back with saying all the boxes I've installed need replacing with "firelined" boxes because their is a fire risk because of the celotex in the wall.The sockets are all on an 30ma RCD, The customer has come back to me and is asking if I did a bad job and I've been trying to find some clarity on this, does their need to be more fire protection round all the sockets??

any help would be greatly appreciated
 
I think you should start with having a look at the building regulations and possibly ask building control about it.
 
  • Like
Reactions: Davisonp
Was there no specification of the refurbishment ? how many sockets are affected ? What is the gap ?
 
So you have a gap between the front plate and back boxes and it sounds like you have a large gap. I agree with the person who did the Report although I may have worded it differently.
 
I'm going to go back later this week to look what the gap is, but as far as I remember it the boxes made it to the insulation but there is the depth of the insulation and plasterboard to the faceplate.
 
You can put fireproofing in the boxes retrospectively and comply with the requirements quite easily. There are two types I know of, one is a kind of putty you mould into the box and the other is a mouldable fireproof material you tuck into the box. I think Part P apply to domestic. As a matter of interest what are the boxes you installed made of ?
 
  • Informative
Reactions: Davisonp
I think the issue is that of the accessory & connections not in an appropriate enclosure as ruston posted if you can fit extension boxes would be the ideal solution.
 
  • Agree
Reactions: Des 56 and ruston
I've used 45mm steel boxes already.
I spoke to the builder who was in charge of the job and he's told me that building regs have no requirement for fire rating of any kind as far as the wall in question is concerned as it's onto an outside wall the ceiling above goes beyond boarding and has only an uninhabited attic above and thinks the guy who put this down is an idiot....

Though I've looked into the extension boxes and I like that solution so for my peace of mind I'll stick them in,Thank you for the help guys.
 
  • Like
Reactions: ruston
As said outside enclosure so got reasonable point we have to fit these not because the council clerk of works likes them as we have boxes when double boarded needs them likes to see metal box flush with surface.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Back box fire ratings
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
ravingmadrongo,
Last reply from
Toneyz,
Replies
9
Views
8,917

Advert