Hey up,

I've got to fit 2 2x58W fluorescent fittings surface mount no access from above but the fittings have besa mounts on rear. Cable will be in plastic conduit.
Will the besa boxes support the fitting weight?
Do you put 4 boxes on the ceiling then hold the fitting on these using the lids?

Ive never attempted this method before but they seem a bit flimsy with the small screws etc.

Is there a better method?

cheers as always
 
you will be able to mount those fittings on plastic terminal, ends, tees, throughs or angle boxes which ever suits your needs. The weight on the M4's will not be an issue if you use a washer inside the fitting, your only issue will be the fixings you use for your plastic tube install.
 
As said, the important thing is the fixing of the boxes to the ceiling, the M4 screws will easily hold the weight of the fitting.
Don't nip the M4s up too tight though with plastic conduit boxes. Sometimes the brass inserts can pop out if tightened too forcefully on cheaper conduit boxes.
 
excellent thanks guys.

Do you guys run a piece of empty conduit between the 2 boxes to make it neater rather than having a terminal with nothing in it?
 
Yeah, if a straight run then i would have a through box to end box 600mm apart, for no real reason other than preference i would run the cable through to the end box and so through that piece of conduit.
 

Reply to besa boxes surface mount fittings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An odd question granted but bear with me. I've got to extend a radial circuit in a community centre to fit a new hand dryer in the toilets, but I...
Replies
15
Views
3K
I am connecting a manual transfer switch to a subpanel. In order to minimize drywall work, I am mounting the transfer switch to the surface of the...
Replies
3
Views
1K
Hi all, Disclaimer: I'm not an electrician and have very basic knowledge of electrical installation. We've been putting in a new kitchen into an...
Replies
17
Views
2K
I know this is a bit of an odd one, so bear with me, I have an idea in mind, but many of the power strips I see are either a) crap b) stupidly...
Replies
15
Views
3K
anyone know of a white surface mount 2 gang box with side entries ? 20mm round conduit radial around garden office, plenty of top entry ones about...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock