Deleted member 9648

Staff accommodation in a large hotel, was asked by maintenance guy to look at a DB. MK board with 3x RCBO's serving rings, and the rest lighting MCB's. One of the RCBO's was making a very noticeable buzzing noise,but otherwise worked fine. Disconnected cables and the buzzing stopped, IR circuit...nothing untoward. Reconnect cables and the buzzing starts again...with or without load. Was going to go and pick up a replacement straight away, but maintenance guy insisted on leaving it to the morning as he was already overtime.... 'and anyway,it's been like it for weeks'!

Any suggestions as to the cause of the buzzing?
 
try switching the circuits from the buzzing RCBO with another. if the buzzing stays with the original RCBO, replace. if it follows the circuit, then it's a circuit problem. one other possibility is to move the RCDO position so as to be next to a different device than the one it's next to at present (harmonics).
 
Thanks fella's.....didn't have a lot of time as I said....it was last knockings after an afternoon repairing hot cupboards in the hotel, but definitely not overload as it did it with no load at all. I suspect faulty RCBO, will find out in the morning.....just seems odd that as soon as cables disconnected it stops,and clamp meter showing zero amps on the circuit
 
Is this buzzing RCBO for a lighting circuit and are the lights dimmed ??? - swap the dimmer out with a normal switch and see if it stops.
 
As already mentioned, high load current and some kind of PWM electronics such as dimmers or maybe a fan speed controller etc are the causes I've come across. As per Tel's suggestion swap the circuits or even RCBO's around and see if the buzzing follows one in particular. I had a similar problem with an MCB once and two new replacements did exactly the same, I had to use a replacement from a different manufacturer eventually. There was obviously a compatibility issue with something on the load side that caused resonance with that particular MCB design.
 
Staff accommodation- could be a rogue Rampant rabbit.:confused::laugh3:

He said it was a ring...which means the pleasure aid you speak of,is corded...

I make it a rule,not to use a mains powered device of this type...caused a right mess last time...:wings:
 
Oooer Missus!.......we've gone a little off piste so to speak!.......will have a check for rampant rabbit chargers tomorrow and will report back on how the replacement RCBO fares.
Thanks for all the replies chaps.
 
If you can't measure any real load on the circuit, but yet can't prove conclusively everything is disconnected, it does strongly suggest phase-angle control turned down low like Darkwood's lighting dimmer (perhaps a standard lamp with inline dimmer) But also possibly something electronically controlled that isn't supposed to be variable in which the triac is barely firing (fan timer?), or even the internal ballast of a dead CFL or a faulty SMPSU with one half of its rectifier open-circuit. I can think of all sorts of electronic things that might be persuaded to generate a load current waveform that would buzz the current coil of an MCB but look open-circuit to a multimeter continuity test. How about an internally arcing delta-cap in an appliance - usually still in circuit with the appliance off. That probably wouldn't last long without going bang though.

It'll be interesting to hear the outcome...
 
Update.
Swapped the RCBO this morning and the new one buzzed exactly the same. Unfortunately there was no access to the rooms untill tomorrow morning so further investigation had to wait but at least the possibility of a faulty breaker has been eliminated.
Thanks again for the suggestions of causes,will be going round tomorrow unplugging/disconnecting loads and try to pin it down that way. If that doesnt work some more extensive testing may be required.
 
It's the kind of issue that you'll probably find by elimination, ie unplugging or disconnecting loads rather than actual testing. TBH if RCBO is not getting warmer than usual I wouldn't worry about it, it's not something that's likely to be a safety issue, just an anomaly or an annoyance at worst.
 
Sorted.
Tracked down an FCU on the ring serving two high level son floods, neither of which have apparently worked for some time. As soon as these were disconnected the buzzing ceased and resumed when re-instated. I'll leave the technicalities of how these affected the RCBO to those with more technical knowledge than myself,as no further investigation was carried out. They were left disconnected pending replacement with 50w LED floods.
 
Possible the striker constantly trying to strike a duff lamp at a guess or a ballast sat energised generating a few transients back down the circuit... like I say just a guess.
 
Last edited:
Aha so I was fairly close with my florry ballast suggestion. I'm with DW it was probably the igniter just breaking over, generating nice little current spikes without using any real power. Glad you found it.
 
Sorted.
Tracked down an FCU on the ring serving two high level son floods, neither of which have apparently worked for some time. As soon as these were disconnected the buzzing ceased and resumed when re-instated. I'll leave the technicalities of how these affected the RCBO to those with more technical knowledge than myself,as no further investigation was carried out. They were left disconnected pending replacement with 50w LED floods.
Glad you found it and thanks for letting us know, it's one of those little interesting ones I'll remember for next time I get a buzzing protective device.
 

Reply to Buzzing RCBO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
732
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
461
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
1pm, quite happy doing my planned job. Builder then asks if I could go out to another job where the top lights have all tripped out. I like peace...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock