i am just a little unsure if i need to use 5 seconds as my D/T or 0.4? PFC obtained through Ze test at origin.

i have been told 2 different answers and any guidance would be helpful.

thanks james
 
On TN systems the maximum permissable disconnection times are 0.4s for final circuits up to and including 32A. 5s for distribution circuits and final circuits over 32A.

For TT systems it is 0.2s and 1s respectively.

If you are trying to work out the 't' in an adiabatic equation then you should be using manufacturers data or at worst the regs book and the time current graphs to tell you what the D/T will be for the OCPD when exposed to the PEFC you have measured. Using 0.4 or 5s for your calculations will more often than not give you an earthing conductor size which is far higher than required.
 
Last edited:
You need to work out the 'S' in the adiabatic for the size of your conductor, not t, you cant work out the 't' as this is determined by the maximum disconnection time allowed for the particular circuit, 0.1, 0.4 etc etc and is a constant.
 
The bit i was not sure about is what the max DT is. My PFC is taken at the origin through a Ze test. would this be a distribution circuit and be 5 seconds?

thanks james
 
no. t is the time the ocpd takes to trip with the pfc that you have measured. usually be 0.1sec. taken from appendix3 BGB. time/current curves.
 
its the fault current squared X the disconnection time (0.4 or 5 sec)...apply the square route to that sum then divide the result by the factor of K....which for copper is 115
 
its the fault current squared X the disconnection time (0.4 or 5 sec)...apply the square route to that sum then divide the result by the factor of K....which for copper is 115
. nope, glenn. get the value of t from time/current curves, and k is 143 if it's a single cable like as wot a main earth is.
 
k is 115 in a multicore cable or cables bunched, but it's 143 for a single cable in free air or clipped etc., as it has better cooling.
 
Telex and D are right here. You have to work out using the graphs/manufacture data, the actual time in which it takes the over current protective device to disconnect the current that would flow in the circuit during fault conditions. (PFC) so if the pfc was lower it would take longer to disconnect! And vice versa! Hope this helps!!
 
Telex and D are right here. You have to work out using the graphs/manufacture data, the actual time in which it takes the over current protective device to disconnect the current that would flow in the circuit during fault conditions. (PFC) so if the pfc was lower it would take longer to disconnect! And vice versa! Hope this helps!!
i`m aware of disconnection times....
 
You could just refer to table 54.7 of the regs book, where the sizing of the earth has been calculated for you I believe?
the adiabatic is good for calculating CPC/earth size for singles.....and also to make sure that any CPC within a cable is good for the time/current curves for the particular choice & setting of OPD being utilised...
say you had a ring final where the live conductors were intact but the CPC was broken....however all points served had R2....this is when the adiabatic would come in handy....it would confirm the difference between a pass and a fail.....
 

Reply to calculating main earth size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
712
Hi I have a domestic installation to rewire and the main incoming fuse is 80 amp so i am using 16mm double insulated tails, is the main earth size...
Replies
6
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
523
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
I am an enthusiastic retired engineer rebuilding a barn in France from scratch and am having problems sizing my incoming electrical cables. I have...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock