I'm trying to calculate the volt drop on cables that are over 16mm csa using the tables in BS7671. It's quite easy for lower sized cables, (length x design current x mV/A/m, if I'm right) but what happens when you go above 16mm and have a resistive component mV/A/m(r), reactive component mV/A/m(x) and inductive component mV/A/m(z)? Do I take all of these into account, or just choose according to load type? The regs aren't really very clear on this bit, I'm finding.
 
if you look at table 6E2 in the red osg, page 133, you will see that the mV/A/m includes the reactive elements for cables 25mm and above. so it's a straightforward calculation.
 
mV/A/m(z) = assumed impedance Z= rt(R^2 + x^2)
The assumed loading (current flow) on a large cable will generate its own inductive reactance, so needs to be taken into consideration
 
mV/A/m(z) = assumed impedance Z= rt(R^2 + x^2)
The assumed loading (current flow) on a large cable will generate its own inductive reactance, so needs to be taken into consideration

Ah right, so because mv/A/m(z) is using both the reactive and resistive components to be formulated, this is the value to use in the volt drop calculation.
Thanks.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Calculating volt drop for >16mm cable
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
BillySangster,
Last reply from
BillySangster,
Replies
3
Views
6,109

Advert