B
BillySangster
Hello there.
I'm trying to calculate the volt drop on cables that are over 16mm csa using the tables in BS7671. It's quite easy for lower sized cables, (length x design current x mV/A/m, if I'm right) but what happens when you go above 16mm and have a resistive component mV/A/m(r), reactive component mV/A/m(x) and inductive component mV/A/m(z)? Do I take all of these into account, or just choose according to load type? The regs aren't really very clear on this bit, I'm finding.
if you look at table 6E2 in the red osg, page 133, you will see that the mV/A/m includes the reactive elements for cables 25mm and above. so it's a straightforward calculation.
mV/A/m(z) = assumed impedance Z= rt(R^2 + x^2)
The assumed loading (current flow) on a large cable will generate its own inductive reactance, so needs to be taken into consideration
Ah right, so because mv/A/m(z) is using both the reactive and resistive components to be formulated, this is the value to use in the volt drop calculation.
Thanks.
Calculating volt drop for >16mm cable
BillySangster,
BillySangster,