Caravans – yes really!
Customer asked me to provide a new board and 3 x distribution circuits for “caravans” they will be living in while they redevelop their house.
Initial spec was that the incomer would be TNS and I had planned to fit a main board with MCB’s and then run 3 distribution circuits to each of the vans which were anticipated to be pre-wired with a plastic CU/RCD incomer. This solution would rely on the earth at source
I’ve now discovered that the “supply” is actually a temporary supply and is a TT supply – so I need to think again (fortunately for me I had declined to give a firm price until the incoming supply and caravans had arrived!).
So my thoughts are a bit all over the place and I could do some input as I haven’t done a caravan install like this before – nor have I touched a TT refurb / rewire for about 5 years!
Option A
100ma RCD in main board (its metal clad for SWA termination) but can’t risk a 30ma to cover the 3 vans!
TT earth for main board
MCB’s for 3 circuits
2 core swa with the armour connected at main board only
TT each caravan so 3 more earth stakes
Option B
100ma RCD in main board (its metal clad for SWA termination) but can’t risk a 30ma to cover the 3 vans!
TT earth for main board and caravans
MCB’s for 3 circuits
2 core SWA but with the armour connected at both ends so caravans rely on single earth stake(s)
Other info!
Also, judging by the cu cables they were previously connected via a blue cable with a commando socket but the loads on 2 of the vans will be above 16 amps so a more robust supply is needed. Each van has a 32A RFC and a 6A lighting circuit.
Thoughts and input appreciated.
Thanks
Customer asked me to provide a new board and 3 x distribution circuits for “caravans” they will be living in while they redevelop their house.
Initial spec was that the incomer would be TNS and I had planned to fit a main board with MCB’s and then run 3 distribution circuits to each of the vans which were anticipated to be pre-wired with a plastic CU/RCD incomer. This solution would rely on the earth at source
I’ve now discovered that the “supply” is actually a temporary supply and is a TT supply – so I need to think again (fortunately for me I had declined to give a firm price until the incoming supply and caravans had arrived!).
So my thoughts are a bit all over the place and I could do some input as I haven’t done a caravan install like this before – nor have I touched a TT refurb / rewire for about 5 years!
Option A
100ma RCD in main board (its metal clad for SWA termination) but can’t risk a 30ma to cover the 3 vans!
TT earth for main board
MCB’s for 3 circuits
2 core swa with the armour connected at main board only
TT each caravan so 3 more earth stakes
Option B
100ma RCD in main board (its metal clad for SWA termination) but can’t risk a 30ma to cover the 3 vans!
TT earth for main board and caravans
MCB’s for 3 circuits
2 core SWA but with the armour connected at both ends so caravans rely on single earth stake(s)
Other info!
Also, judging by the cu cables they were previously connected via a blue cable with a commando socket but the loads on 2 of the vans will be above 16 amps so a more robust supply is needed. Each van has a 32A RFC and a 6A lighting circuit.
Thoughts and input appreciated.