Marvo
I think the 1667 ohm ceiling is purely safety related and derived from disconnect times in the case of a fault. I'd suggest it would be a professional approach to consider the functionality aspect of the earth as well which would involve looking how well it would perform for surge arrestors and noise suppressors etc in electronic equipment that might be plugged into the final circuits. On this occasion I'd be in the NICEC camp and striving for a stable sub 100ohm Ra or even lower if possible.