I think the 1667 ohm ceiling is purely safety related and derived from disconnect times in the case of a fault. I'd suggest it would be a professional approach to consider the functionality aspect of the earth as well which would involve looking how well it would perform for surge arrestors and noise suppressors etc in electronic equipment that might be plugged into the final circuits. On this occasion I'd be in the NICEC camp and striving for a stable sub 100ohm Ra or even lower if possible.
 
I think the 1667 ohm ceiling is purely safety related and derived from disconnect times in the case of a fault. I'd suggest it would be a professional approach to consider the functionality aspect of the earth as well which would involve looking how well it would perform for surge arrestors and noise suppressors etc in electronic equipment that might be plugged into the final circuits. On this occasion I'd be in the NICEC camp and striving for a stable sub 100ohm Ra or even lower if possible.
Obviously a reading under 1 ohm is what we would like to achieve, the NICEIC do not write the regs book though and 200 ohms satisfactory to the book, personally I would not be anywhere near satisfied at that reading but the regs are the regs.
 
UPDATE

So I did the work today - with 2 meters of 5/8 rod - 1233 ohms - 3 meters of 5/8 rod it came down to 168 ohms, 4 meters of 5/8 it came down to 113 ohms.

Added a 2nd rod at one of the vans (2 meters) and it didn't improve, and it was getting dark - so I'm going back next week with more rods and more couplers!

Sounds fine to me, i wouldnt get to hung up on acheiving a really low Ra, stable will do, by the way, the more you bang in the less effect it has of lowering the Ra, it all becomes a little fruitless.

Cheers
 
so what is wrong with 80 ohms? obviously not the reading you would like but well within the limits to the regs Book
 
UPDATE: A couple more rods and the reading is now 80 ohms.

So I gave up!

Perfectly fine, well done.

You can only work with the ground you have. Now if naturally the resistance is high then you have little chance of acheiving low values, remeber high values can be stable too and stable is the important bit.

Cheers
 
  • Like
Reactions: 1 person
the problem with the TT is that although each pitch is protected by a 30mA RCD, the distribution cable ( even if SWA) requires a RCD upfront to comply with disconnection times.
 
discrimination between RCDs.
 
probably, not always.
 
UPDATE: A couple more rods and the reading is now 80 ohms.

So I gave up!

A Spark using proper rods got 80 Ohms??

Me - a plumber (sort of) - got exactly that from a bit of 15mm copper tube hammered into the lawn!! :sailor:
 
A Spark using proper rods got 80 Ohms??

Me - a plumber (sort of) - got exactly that from a bit of 15mm copper tube hammered into the lawn!! :sailor:

trust you to try and bypass your water meter. :juggle2:
 
maxresdefault.jpg
 
  • Like
Reactions: 3 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Caravans - yes really - going round in circles....
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
Octopus,
Last reply from
Geordie Spark,
Replies
36
Views
328

Advert