Currently pricing a rewire for a two bed terraced house and just wondered on people thoughts on fire detection. I am going to install mains powered with battery back up and was thinking of :-

1 x heat detector in kitchen
1 x smoke detector in living room
1 x smoke detector on landing

Should i include a carbon monoxide detector as there is a combi boiler in the kitchen. Already spoke to a couple of people for there advice and both have said that wherever there is a fuel burning device ( boiler, log burner etc ) they should be fitted.
 
Currently pricing a rewire for a two bed terraced house and just wondered on people thoughts on fire detection. I am going to install mains powered with battery back up and was thinking of :-

1 x heat detector in kitchen
1 x smoke detector in living room
1 x smoke detector on landing

Should i include a carbon monoxide detector as there is a combi boiler in the kitchen. Already spoke to a couple of people for there advice and both have said that wherever there is a fuel burning device ( boiler, log burner etc ) they should be fitted.
Are you sure about the heat detector in the Kitchen?
 
As a minimum smoke in hall and landing and a heat in the kitchen. If you install a carbon monoxide alarm you want it to make a different noise so you can distinguish between carbon monoxide and fire.
 
Just been doing some research on mixing CO and smokes on the same interlink. It's a no go if the alarms do not make a different sound throughout the system to differentiate what type of event it is.
I think Kidde firex offer this multi-tone solution.
A solution with Aico is to fit a control switch which hushes all alarms when pressed except the triggered head. These switches are available wired or wireless.
Another solution is to have the CO as battery only.
 
  • Like
Reactions: Rpa07
Is the kitchen separated from the stairs or landing/hall (circulation area) by a door? If not, there must be a heat alarm in the kitchen. However, I always fit them regardless.
 
Just been doing some research on mixing CO and smokes on the same interlink. It's a no go if the alarms do not make a different sound throughout the system to differentiate what type of event it is.
I think Kidde firex offer this multi-tone solution.
A solution with Aico is to fit a control switch which hushes all alarms when pressed except the triggered head. These switches are available wired or wireless.
Another solution is to have the CO as battery only.
The system in my house uses Kidde Firex (older ones), the CO alarm is on the same circuit but not interlinked. The reason I didn't interlink at the time was (I think) it operated at a different signal voltage to the smokes and wasn't compatible? My memory is a bit sketchy though.
 
Just been doing some research on mixing CO and smokes on the same interlink. It's a no go if the alarms do not make a different sound throughout the system to differentiate what type of event it is.
I think Kidde firex offer this multi-tone solution.
A solution with Aico is to fit a control switch which hushes all alarms when pressed except the triggered head. These switches are available wired or wireless.
Another solution is to have the CO as battery only.
I have looked into this before and wondered why carbon monoxide and smoke detectors could not be on the same interlink. Am i right in thinking that depending
on what alarm has been activated different action should be taken. Im sure i read that in the event of a carbon monoxide alarm activating then you would open doors, windows etc to ventilate the area whereas if it were a smoke alarm that had been activated you would want to keep doors and windows closed? What other reasons can they not share an interlink for?
 
I have looked into this before and wondered why carbon monoxide and smoke detectors could not be on the same interlink. Am i right in thinking that depending
on what alarm has been activated different action should be taken. Im sure i read that in the event of a carbon monoxide alarm activating then you would open doors, windows etc to ventilate the area whereas if it were a smoke alarm that had been activated you would want to keep doors and windows closed? What other reasons can they not share an interlink for?

Yes exactly that. The alarm should distinguish which event has taken place so that appropriate action can be taken.

If all heads make the same sound no matter what the event this is not suitable.
If CO and smoke make different sounds, but they only make their individual sound no matter what event this is not suitable.
 
Yes exactly that. The alarm should distinguish which event has taken place so that appropriate action can be taken.

If all heads make the same sound no matter what the event this is not suitable.
If CO and smoke make different sounds, but they only make their individual sound no matter what event this is not suitable.
But surely the first action you should take would be to get out of the property? It wouldnt matter which alarm had gone off if you were not inside
 
  • Like
Reactions: DPG
But surely the first action you should take would be to get out of the property? It wouldnt matter which alarm had gone off if you were not inside

Now you're talking about common sense. I thought you were talking about regulations and liability of the installer. Those are very different things.
 
  • Like
Reactions: Richard Burns
Now you're talking about common sense. I thought you were talking about regulations and liability of the installer. Those are very different things.
Ha ha of course. Back to the OP though does the situation ive described need a carbon monoxide detector? The kitchen is very small and fitting two devices on the ceiling isnt going to look very attractive.
 
I fitted a carbon monoxide alarm in my house, interlinked with smokes, some years ago. The cmd has a small digital screen, and indicates 'Fire' if it is one of the smokes that have activated. They are nearing replacement.

Alternatively, as Andy suggested use a remote control switch. If the customer doesn't want two devices on the ceiling in the kitchen, a small cmd battery operated one could be installed separately, somewhere adjacent to the boiler.

Edit; why not ask Aico, one of the forum sponsors?
 
Last edited:
In Scotland for private let accommodation you must have, by law, a smoke in livingroom, hall up and downstairs (if applicable) and a heat in the kitchen. Mains operated and inter linked.

As for carbon monoxide alarm, this can be battery operated as long as it's a sealed unit with a 7 year life span.
 
yes i dont see why not, wouldnt want any false alarms from burnt toast etc. If im wrong please point me in the right direction
Hi Mate my reason was if your Kitchen is anything like mine, it gets hot really hot, your not wrong just my personal thoughts
 
Afaik we must have CO alarm where there is a log burner, fuel stove etc, and recommended for each location with a gas burner.
 
i'd fit interlinked smoke and heat alarms as you suggested, but a battery only free standing CO alarm. this could just be placed unobtrusively near the boiler.
 
In my own house, in addition to the mains CO alarm in the kitchen (where the boiler is located), I have battery detectors in our bedroom and our son's bedroom. I am a bit paranoid though. The owners of a nearby Chinese takeaway lived in the flat above the shop and the whole family were killed my CO from the boiler. It hadn't been serviced in over ten years though, apparently. My interlinked smokes are OTT as well, I have ten. :oops:
 
In my own house, in addition to the mains CO alarm in the kitchen (where the boiler is located), I have battery detectors in our bedroom and our son's bedroom. I am a bit paranoid though. The owners of a nearby Chinese takeaway lived in the flat above the shop and the whole family were killed my CO from the boiler. It hadn't been serviced in over ten years though, apparently. My interlinked smokes are OTT as well, I have ten. :oops:
bloodyhell. that lot go off it'll wake the dead. get on dragon's den with it.
 
Install a carbon monoxide detector in a central location in your house. The CO detector should be about 5 feet from the floor. The reason is that this chemical compound will rise as the temperature in the air within the vicinity rises.
Additionally, make sure that the device is close to your sleeping quarters to hear the beep if it detects the odorless and colorless gas. This way, we can be aware of CO levels and gas leaks.
 
Co alarms need to be fitted on the ceiling within 1-3 metres of a fuel burning appliance or flue. As an extra one sitted at the height your head is, where you spend a lot of time . Ie: on the sofa or in bed.
 
Old post.

Be aware that the US and UK guidelines may differ
 
  • Like
Reactions: DPG
Currently pricing a rewire for a two bed terraced house and just wondered on people thoughts on fire detection. I am going to install mains powered with battery back up and was thinking of :-

1 x heat detector in kitchen
1 x smoke detector in living room
1 x smoke detector on landing

Should i include a carbon monoxide detector as there is a combi boiler in the kitchen. Already spoke to a couple of people for there advice and both have said that wherever there is a fuel burning device ( boiler, log burner etc ) they should be fitted.
CO Alarm should be installed at least 20 feet (6 meters) away from the furnace or fuel burning heat source. We think Gas leakage detector with solenoid valve should be installed in kitchen.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

leep82

Arms
~
Joined
Location
Stoke on Trent
Business Name
L.M.P Electrical

Thread Information

Title
Carbon Monoxide Alarm
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
leep82,
Last reply from
vedardalarm,
Replies
23
Views
4,887

Advert