Small private building site. I'll be setting up the temporary supply soon.
TT then small RCD garage unit inside the meter box on a post (DNO agrees that OK), and couple of IP66 sockets under. All good.
But customer also has a titchy site caravan alongside. - Sect 708 calls for INDIVIDUAL 2-pole RCD for each caravan supply. This complicates an otherwise neat little job.
Bearing in mind main RCD in CU is 2 pole, and demand limited to a computer and kettle, might you go for 13A plug to BS EN 60309-2 adaptor (about £5) for the caravan cable? (For a rather minor BS7671 infringement)?