after changing a board and doing a eic, do you put in the note that its just a change of board. what i mean by this is i wont of check things like conductor id,will be upgrading tails/bonds,
i will do a i.r befor to check that no probs!
cheers guys!!
 
I think we are talking about the schedule of inspection part of the form. a 'X' would indicate a fail which can only be done on a PIR if it's non applicable then it's a N/A.

But even then on the original post identification of conductor should be ticked, as when the board is reconnected your ensuring that the LINE, NEUTRAL and CPC are indentified by colours.
 
I agree with Malcolm, an EIC is for the work you have done and by putting an X in a schedule of inspections box you are infact failing your own work.

After changing a board, in the "extent of the installation covered by this certificate" box, you simply put - upgrading of consumer unit only.
 
Hi All
If you change a consumer unit and one of the ring circuits are found to be faulty lets say the CPC's aint continuous then shouldn't you put it right rather than note it in the comments
 
you should rectify any fault/potential safety issues found, but will the customer pay for the extra work. i alweays explain to the customer when i quote, that gthe quote is for CU replacement, and if any faults are found during the job, their rectification will entail further costs. i try and put this gently so as not to scare them off having the job done. IR test, and checking for borrowed neutrals at time of quoting is a must, IMO
 

Reply to change of board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

When doing an eic, does anyone put limitations for existing wiring within walls and under floors and you’re not able to check them? Or what do...
Replies
5
Views
943
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hey guys, Im starting to put my company out there more. And this is all a new journey for me being an apprentice and now being qualified/2391-52...
Replies
25
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock