I am thinking the installation was a TNS conversion to TNCS, and the 6mm was fine for the original design. DNO updates to PME and now it's not in accord with BYB.
On the bonding, I think electrical installation starts where the cutout / meter is and the bonding should be where the pipe enters the the location served by that installation, rather than at some other location on the property. But I'm very happy to learn if it's other