In that case not sure what grounds you’ve stated unsatisfactory.

what is the actual reason stated for the coding? And what code did you give?
I went with a C2 Recommended cable change to 3 core and standard S/O plate. Posted this because I've never seen this setup and it just felt wrong.
 
I went with a C2 Recommended cable change to 3 core and standard S/O plate. Posted this because I've never seen this setup and it just felt wrong.
I get what your recommending, but what is your reason for the coding?

in an EICR observations you don’t put what should be there or what should be done. You put what is wrong At the time of inspection.

examples:
disconnection times not achievable due to……

potential for overload because…….

cable not sufficient current carrying capacity due to……

etc….etc…


What was the actual wording in observations for your C2?
 
I get what your recommending, but what is your reason for the coding?

in an EICR observations you don’t put what should be there or what should be done. You put what is wrong At the time of inspection.

examples:
disconnection times not achievable due to……

potential for overload because…….

cable not sufficient current carrying capacity due to……

etc….etc…


What was the actual wording in observations for your C2?
The C2 was simply recorded as not complying with 411.3.3 "Additional Protection by means of an RCD" The recommendation to the customer was cable and S/O change.
 
So i should change fuse in the FCU to 200 mA from 13 to comply ?
If it is a standard transformerless shaver socket outlet, then it is automatically restricted to 200mA internally, the upstream fuse merely needs to be sufficient to protect the cable.

If it is not a transformer or tranformerless shaver socket outlet to bs4573 it is not permitted.

The only socket outlets permitted are those detailed in the regs, ie bs1363, 546 etc.

This isn't just the regs that mandate this, it is actually law SI 1768 1994 - plug and socket regulations.

This is freely available on-line , if you do have a 2 pin eu or similar plug, then the adapter must be included, must be to standard/approved, includes a fuse, and cannot be removed without tools or may have proper shutters etc.
 
The C2 was simply recorded as not complying with 411.3.3 "Additional Protection by means of an RCD" The recommendation to the customer was cable and S/O change.
I'm late to this interesting party, and by heck it took a while to get going too!
So if I can be excused for buying a round of drinks and shoving a quid in the juke box after midnight.....I don't get why no one is mentioning 411.3.1.1 - having no CPC as required to each point in wiring and each accessory.
I'd have thought it was just a simple C2 for that in addition to the RCD issue? Even if the CPC ends up not going anywhere, the only dispensation in the regs for not having one at all that I'm aware of is lamp holder.
Any rate - I'm glad it was coded, needs sorting.
 

Reply to Class 2 Spur to outside socket in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
643
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
389
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
799

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock