whether there's a cpc or not, damage could result in exposed live parts without ADS occuring, so what is the point of a cpc running alongside the L conductor? a an;t see any reg, breached whatewver.note in the comments sesction is all i'd put, just to show that i'd spotted it. c
 
this was my initial point of view. I suppose you could argue that you are increasing the protection even though it may not actually work in practice. I have read through section 4 quickly but I just to tired to take it in. have a read when a bit fresher.
 
If you believe that it is likely to suffer damage then perhaps pvc conduit is not the correct containment rather than wanting a cpc which is not required and would not afford any protection.
 
If it doesn't work in practice then you aren't achieving anything.

If you are going to put this down as an observation requiring any action on an EICR then you need to be able to justify it in the regulations. There is no regulation requiring a cpc to be run alongside every conductor, only one that requires the cpc to be contained within the same wiring system.
 
I can't see any breach of the Wiring Regulations unless it was to enter a ferrous enclosure on its own at some point.
It does enter the light fitting which is ferrous but as I said earlier all other points are earthed, so a short there would result in the protective device tripping.
 
Only if it entered the fitting through a different hole to the CPC and neutral.

I combed through my local SA regs just out of interest and there's also nothing that specifically forbids a single live insulated conductor in its own conduit unless you can class conduit as a sheath as well as containment.
 
It's a requirement of the Regulations that all conductors (including the CPC) of a circuit a within the same ferrous magnetic containment (if used).
As this conductor is not within a ferrous magnetic containment it is not required to be within the same containment as any other circuit conductor.
No it does not require another CPC to be run with it either.
 
  • Like
Reactions: 2 people
I'm in a Cafe.
I don't carry copies of the Regs around with me.
If I recall correctly, it's 521.5.2.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
Not sure if this is the exact wording:

Single-core cables armoured with steel wire or steel tape shall not be used for an a.c. circuit. The conductors of an a.c. circuit installed in a ferromagnetic enclosure shall be arranged so that all line conductors and the neutral conductor, if any, and the appropriate protective conductor are contained in the same enclosure.

Where such conductors enter a ferrous enclosure, they shall be arranged such that the conductors are only collectively surrounded by ferrous material.

It's not actually a Cafe, it's an Ice Cream Parlour.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
cpc in pvc conduit?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
34

Advert

Thread statistics

Created
Cazmac1,
Last reply from
Cazmac1,
Replies
34
Views
8,415

Advert