I've always wondered why BS7671 states that a disconnection time of 0.4s is required for circuits NOT exceeding 32A and for circuits exceeding 32A it is 5s

Surely you would want the higher current to trip quicker?

Can someone clarify this?
 
I've always wondered why BS7671 states that a disconnection time of 0.4s is required for circuits NOT exceeding 32A and for circuits exceeding 32A it is 5s

Surely you would want the higher current to trip quicker?

Can someone clarify this?

It was explained to me like this:-

First you need to understand that the 5 second and 1 second times (TT) are not based on the touch voltage curve.

They represent achievable values in that such disconnection times can be met.

Consider a TN system - we are addicted to the use of overcurrent protective devices for fault protection. This requires a substantial current flow to operate the device in a reasonable time. If we consider high current circuits, such as distribution circuits rated at say, 100OA, we need a very low impedance to allow sufficient current to flow to operate the overcurrent device. If we want to operate it quickly this impedance must be as low as possible.

We start to reach the limits with these high current circuits and all we can do is extend the disconnection time to try and make things fit.

5 seconds is a reasonably short time to allow a dangerous voltage to exist on a circuit that is unlikely to actually be in a fault state. i.e. A high current distribution or final circuit is usually fairly robust and faults are not very likely. If a fault should occur there is only a small probability that some one would actually be touching the circuit. Contrast this to a small final circuit that might be supplying something that we actually hold on to such as a power tool.

We could get round this by using RCD or similar technology for fault protection but we usually don't http://www.------.org/forums/forum/i/expressions/face-icon-small-shocked.gif.

TT is a different problem - we are already using RCD's or similar but we need a reasonable time span to achieve discrimination over a large installation. This can mean the use of instant, fixed time delay and adjustable time delay devices in series. 1 Second gives us the required time span.
 
Fantastic in depth answer

thank you IQ!!!;)

So am I correct in saying that any circuit in a TN installation that does not exceed 32A should be 0.4s and above 32A should be 5s?
 
What about a cooker circuit rated 40 amp with a socket on the cooker control ? :)


interesting..... be first to admit, i don't know the answer to this one. however, i would be inclined to enter 5secs. on a test sheet.
 
Personally I would go for 0.4 as there is a socket outlet on the circuit.


Sent from my iPhone using Tapatalk
 
3-2 to 0.4 at half time ( half time being related to TT systems, LOL)
 
I would say 5s as it is the fixed wiring you are protecting and a 40A cooker circuit should have a feed of 10mm realistically. If there is a problem with whatever you are plugging in to the attached skt then surely the fuse in the plug is considered the primary protective device
 
Alright Socket Outlet 0.4 with Additional RCD protection.

Yes, as I said above but the disconnection time on the schedule of test results would still be recorded as 5 seconds whether the installation was under control of instructed/skilled persons or not.
I have a mail from IET technical help confirming this, I'll see if I can dig it out!
 
Yes, as I said above but the disconnection time on the schedule of test results would still be recorded as 5 seconds whether the installation was under control of instructed/skilled persons or not.
I have a mail from IET technical help confirming this, I'll see if I can dig it out!

Didn't realize you was discussing what to put on the test paper, but I would still stick 0.4 in because there's a socket on the circuit, but that's just me I suppose.
 
Be careful how you interpret BS7671, it is not for example a requirement for circuits over 32A or a distrbution circuit to disconnect in 5 seconds 411.3.2.3, it is a permitted increase fundementally to allow discrimination to be achieved
 

Reply to Disconnection Times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K
Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
905
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
516
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock