Hi Guys

Have installed a new CU at clients house. The new CU is on the other side of the building so all circuit tails have been moved. On Tuesday the DNO are coming to install a new supply and meter on the new CU.
I've tried to call the them to ask what exactly they want from me on the day of hook up. I've done an EIC to the best of what I can do, but can't do any live tests until they come and switch on.
Has anyone else had similar experience? I just want to be prepared for the client.

Simon
 
Hi Simon,

In a recent domestic installation where the property was derelict, the DNO wanted to see an EIC (dead tests) along with a schedule of the installation with CCU hung and meter tails left out for them to connect. DNO was SSE.

For a commercial one, they wanted a metal clad main isolator with the SWA feeding the DB glanded along with EIC (dead tests) and installation. DNO was EDF
 
wow.
generally i connect the tails into the cutout and tell them to let themselves in and crack on as ive better things to do than wait for them to decide to turn up when they want.
each to their own i suppose.
everythings always working when i get there?
 
Thanks gents.

Sounds like I'm set. All I've got to do is move the earth electrode from old CCU to new CCU. (and remember to test earth electrode resistance. )
 
Thanks for your help guys.

DNO came in, saw my EIC put a meter in and cleared off and left it to me. It was a nightmare job, but thats a different story.
 

Reply to DNO hook up in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
799
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
391
I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
3K
On another forum for general EV chat this question comes up all the time. It's very common to install a charger taking the supply direct from the...
Replies
14
Views
2K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
836

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock