Hi,
Say i have a 16A load on a Mains 16A circuit at 230VAC.
If its not power factor corrected, then is there a danger the breaker could trip? (due to the reactive current being high aswell).
 
Short answer = Yes

Breakers and fuses look at Irms and will trip on sufficient overload. However, most reactive loads have a significant inrush current as well so the rating of over current protection has usually to have a certain factor above the current you might compute from P/V (even allowing for typical PF)
 
MCBs respond to current. A 16A load is a 16A load, it doesn't matter what the power factor is. That only shows how much real power you get from the 16A and the MCB doesn't know or care about power.

Re. RMS, the overload (thermal) element of the MCB responds to RMS current because it operates on the heating power of the current in a resistive element. But the instantaneous trip (magnetic) element responds more closely to the mean current because it operates on the force exerted by a solenoid, in which the power dissipation is unimportant.
 

Reply to Do Breakers trip on irms(total) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
828
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
283
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock