hi need some advice does this supply head need changed because it looks vintage also are these meters even to be used anymore ?
Last edited by a moderator:
Discuss Does this need replacing in the UK Electrical Forum area at ElectriciansForums.net
Thanks buddy a job for the dno then?The head needs replacing or repairing.
Not because it is vintage but because the neutral terminals are exposed.
Thanks buddy a job for the dno then?
Thank you will get in contact with them tomorrowYes, definitely. That supply cut out is their property and responsibility to maintain.
Good plan, Nice one.Thank you will get in contact with them tomorrow
Well spotted thanksThe main body of the cutout is broken away above where the Neutral cover would be, probably because it's been hit with something, so a new cover wouldn't stay on if the DNO have them as spares.
There's nothing wrong with the meters as long as the Energy Supplier is happy with them.
The cast iron cover leaning up below the meters probably has an asbestos seal in it.
Reply to Does this need replacing in the UK Electrical Forum area at ElectriciansForums.net