Discuss Earth Fault Impedence in the Australia area at ElectriciansForums.net

L

Loyal

Can anyone please explain what is the maximum earth fault loop impedance permitted for moulded case circuit breaker (MCCB)?
Also, BS 7671 says a disconnection time of 5 sec is allowed for breakers in distribution circuits. What is the difference between a distribution circuit and final circuit?
 
it depends on the rating of the protective device.

a distribution circuit is one that supplys another consumer unit or distribution board.
A final circuit is one that would supply the final equipment ( lighting, motors, appliances ect)
 
distribution circuit is a circuit suppling a c/u sub mains etc
final circuit is a circuit supplying like a light - socket - cooker - motor circuit it does exactly wot it says on the tin final circuit from c/u where it usualy has an end point :cool:
 
Thanks for help about the distribution circuits.

I undrstand that the values of Zs as mentioned in table 41.3 of BS 7671 are the same for MCB and MCCB, is it correct?

Also, Table 41.3 provides Zs for breakers up to 125A only. I need Zs for larger breakers (150A, 200A, 300A, etc). Where can I find Zs for the larger breakers?
 
Blimey. Big !
If they are not in BRB (dont have mine to hand) i think you will have to get in touch with manufacturers...!?
 
If I have a circuit breaker with a frame size of 100A and a trip of 32A, then shall I have to use the Zs values for 100A or 32A?
 

Reply to Earth Fault Impedence in the Australia area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
620
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
841
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock