Hi All, I'm working on an older agricultural installation (100A single phase) and would appreciate your thoughts on earthing details :)

Main building is TT. Well it is now that I've installed some rods and reinstated it... There is an outbuilding with some pumps etc that I'm also upgrading. It's about 50m away, supplied by SWA from the main building with armour as CPC. I plan to rod the outbuilding and am thinking to combine the 2 earth rod installations by continuing the SWA armour into the sub board in the outbuilding. My thought being to reduce the installation's Ra and improve its resilience. Or should the 2 buildings means of earthing be kept separate?
 
Hi All, I'm working on an older agricultural installation (100A single phase) and would appreciate your thoughts on earthing details :)

Main building is TT. Well it is now that I've installed some rods and reinstated it... There is an outbuilding with some pumps etc that I'm also upgrading. It's about 50m away, supplied by SWA from the main building with armour as CPC. I plan to rod the outbuilding and am thinking to combine the 2 earth rod installations by continuing the SWA armour into the sub board in the outbuilding. My thought being to reduce the installation's Ra and improve its resilience. Or should the 2 buildings means of earthing be kept separate?
Can't see why it would be a problem.
 
  • Agree
  • Like
Reactions: Des 56 and Wilko
Thanks Westie.
Original rod had vanished and bonding was to a bit of copper pipe I found kicked under the basin in the wash area, long since replaced by a plastic supply. Fortunately the old RCD was still functioning and no incidents had occurred. Originally I was asked to help with a new circuit in the outbuilding pump room but it became a bit more.
 
Sounds like a typical farm I fear for my life every time I visit my brother-in-laws farm.
 
have you found the farmer's supply of spare fuses?


upload_2017-6-2_6-32-55.jpeg
 
  • Like
Reactions: Wilko
I wouldn't be surprised if it was underneath that washroom slab somewhere. Here's a boring pic of the new chap. Like a proud parent I am ... I'm not saying Ra yet, cause I'm hoping to break my record with the 2nd building in parallel :)

IMG_0661.JPG
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing for Farm Buildings
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
Wilko,
Last reply from
Wilko,
Replies
7
Views
60

Advert