Hi, just a quick question...

I’m at the stage now where I’m being pretty nosey at other people’s consumer units/supply set ups etc to further improve my understanding and recognition of the different earthing systems found in domestic properties.

The image below was taken at a member of my family’s home. I initially identified the earthing system as being TN-C-S due to the earth cable coming from the neutral side of the suppliers cut-out, but then I noticed the earth rod underneath. I’ve also noticed the heat damage to the earth cable caused by the gas fitter...

Just wondering what earthing system this would be classed as? I’ve done a bit of digging and found this could be due to the property being converted recently from TT to TN-C-S, however I’m not sure if this is the case. The term localised supplementary earth rod has also come up, but I’m too sure about this either.

Any info would be greatly appreciated. Thanks.

C0ED2672-AF4F-4B61-9A32-E4D58054FF9E.jpeg
 
It shouldn’t be both it’s gotta be one or other.
If Tncs is on site,that’s most probably the best option
 
I can’t see how the connector block on the cutout is connected to the CU ? I’m guessing it connected to DNO cable sheath, but how does it get to CU? Or is it another trip to Specsavers for me?
 
Apologies it’s not the best photograph. From what I could see at the time, the earth cable comes from the cut out down to the terminal block you can just about see in the bottom right hand corner. From here there is a 16mm earth running to the consumer unit. The cable from the earth rod is also connected to this terminal block. There is a 10mm bonding conductor on the earth rod also - this runs to the gas pipe.
 
It looks like that cut-out has been upgraded to TN-C-S from TT or PME from TT however you like to put it. It seems no one thought to move the bonding cable from the rod to to the MET.
 
  • Like
Reactions: DPG and evorg88

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing System Query
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
evorg88,
Last reply from
evorg88,
Replies
6
Views
1,371

Advert