Hi Guys,

An elderly customer has just moved into her new flat, unfortunately her heating on E7 doesn't work. The E7 dist board RCD is tripping (probably as it kicks in).
She has two boards, one normal and one E7. The E7 board is feeding three night storage heaters and an immersion heater. All the wiring checks out fine, the heaters are working (tested). What I find strange is that the neutral tails for both boards are commoned at a Henley block BUT when I tried to jump a feed from the live board, the live board RCD trips. The culprit appears to be when the neutral bus bars of both boards are connected directly to each other. What I can't understand is why, when both neutrals main tails are already commoned?

As for the heaters not working I think a time delay RCD may remedy the tripping. Any ideas greatly appreciated!
 
Hi,
Sounds to me like a Neutral fault somewhere. Did you operate or bypass the stat for the Immersion prior to testing. I certainly wouldn't be putting a time delayed RCD in, I would be looking to rectify the fault.
Regards.
 
Hi Clive,
The time delay RCD is to prevent the storage heaters from tripping the RCD when the E7 kicks in. Each circuit has been tested individually and they all work. The problem arose when I tried to jump a supply from the live board to the E7 board.
 
This is where it gets bizarre....
Ramp tested live board RCD....49mA but didn't trip?
Ramp tested E7 board RCD.... 47mA and did trip. (Obviously using temp supply from live board). Both RCDs 30mA 63A units.
 
Sounds like both RCDs need changing if they are allowing nearly over 50% the amount of leakage. Could be the mechanism inside both of them is shot and therefore not allowing for the inrush of all 3 heaters starting at the same time.
 
Hi,

It's quite common to still run banks of storage heaters off an Economy 7 Board or via contactor using the Meter output as the control circuit. I worked on one the other day which switches a number of heaters. Thing was that wasn't a domestic environment, so no nuisance tripping from RCD's.
As Dillb says your' RCD results aren't satisfactory and definitely need looking at.
Your cross-over supply check, well here you have commonned Neutrals on the supply side which is correct, and possible crossed over on the load side depending on what you had isolated at the time ( before the temporary link ). It can sometimes be difficult to envisage the set up without seeing it.

Regards.
 

Reply to Economy 7 RCD tripping. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
864
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
439
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock