• IMPORTANT: Please note that nobody on this forum should be seeking from or providing advice to those who are not competent and / or trained and qualified in their field (local laws permitting). There is a discussion thread on this global industry-wide matter HERE. This also has more information about the warning with regards to sharing electrical advice in some countries. By using this forum you do so in agreement to this.

Discuss EICR and RCD's. Is it a C2 or C3? in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

That's all I have. Apart from a quotation to replace "fuseboard".
So do I spend many hundreds of pounds to replace the Consumer Unit?
Of course ideally ALL Consumer Units in every household should meet current regulations. This is not realistic. The bottom line is C2 (Potentially Dangerous) applicable given the data?

If a number of forum member have a c2 (potentially dangerous) opinion I will change the Consumer Unit.

Thanks for all your feedback....
 
Why would a landlord be responsible for stupid children and lazy parents?
If you have to ask that question then I don't think you'd really be able to understand the answer so probably best not to go into it.
 
You do not base findings in an EICR predicting the actions of a child. Your findings are based upon BS7671 which does not differentiate between a child and an adult.
 
According to the tick sheet there is supplementary bonding in the bathroom so no rcd required there. There is also IR values in L-N column, so everything got disconnected, all lamps removed etc to preform this test - I don't think so.
I would complain to NAPIT as the standard of the report is poor with unwarranted C2s.
All said though a board upgrade is a good recommend.
 
According to the tick sheet there is supplementary bonding in the bathroom so no rcd required there. There is also IR values in L-N column, so everything got disconnected, all lamps removed etc to preform this test - I don't think so.
I would complain to NAPIT as the standard of the report is poor with unwarranted C2s.
All said though a board upgrade is a good recommend.
Supplementary bonding does not remove the requirement for RCD protection of bathroom circuits. 30mA RCD protection of bathroom circuits may well remove the requirement for supplementary bonding though.
 
Without personally inspecting the property it’s difficult to know what has been discovered or missed by the previous inspection. I may issues a code 2, if for example,
1. Socket installed too close to a sink which can potentially be splashed
2. Any signed of water ingress
3. TT earthing system have no RCD protection
4. Outside socket (balconied) or potential to plug in and use an device outside.
5. High Zs reading not protected by RCD
6. No mechanical protected for cables (concealed <50mm, in metal framed partition, or otherwise)
7. Socket within 3m of zone 1
Or any other general safety conserns that want a risk assessment for admission of RCD (reg 411.3.3)

The fact that it’s probably got code 3 5 years ago and the recommendation goes ignored. Most people translate c3 to satisfactory and just ignore then until they get worse or C2s.
 
Last edited by a moderator:
If you have the eicr from 5 years previous did the spark ask to see it? As he’s ticked date of last inspection unknown but you say 5 years?
 
Last edited:
The tick sheet says there is RCD protection for the bathroom circuits.
Q1 it says u have 10 mmm main tails these are usually 25 or 16 min
If they are 10mm this is a C2 as they are undersized
Q2 report says u have AFDDs and surge protection
Defo not
Q3 did he inspect below the floors and above ceilings
Q4 did he carry out R1+ R2 tests as the numbers are exactly ZS-ZE
Q5 cable type 1 on report there is no type 1 it should be A
The values on the report are wrong 5.88 ??
You should send that report to NAPIT and ask for their comment and if possible post the response on the forum,,
The quality of testing is always a question raised ,
There is no rcd test results on his results
And he says there is rcd test notifications labels
 