If it walks like a Duck and quacks like a duck...
 
NO!

Read the definitions of C1 and C2 in the books.
It's written in plain English, 'Immediate' and 'Potentially'.

Calm down dear, I was only asking a hypthothetical question.

I was only asking as if the installation contains circuits with high CPC currrents in normal use then without the main earth then there could potentially be a voltage relative to earth present at all metalwork connected to the CPC in question.
Obviously on discovering an installation with no main earth you would carry out some simple voltage tests to ascertain whether this has led to metal parts of the installation being at a voltage relative to metal objects connected to true earth which are available to touch.

I know its a C2 for no main earth, but if you have no main earth and identify a voltage between a metal DB and the exposed lead sheath of the incoming supply cable as a direct result of this then that could be immediately dangerous (I mean a real voltage not a ghost)
 
Haha...I'm always calm! :)
Say there were raised voltages on Exposed parts, one might expect reports of people getting slight shocks.
Then, obviously, an Electrician would be called in to investigate. Still not an Immediate Danger though.
But in the general case, an install in good condition with a missing Earth, is potentially dangerous in the event of a Line to Exposed part fault, hence....C2.
 
Haha...I'm always calm! :)
Say there were raised voltages on Exposed parts, one might expect reports of people getting slight shocks.
Then, obviously, an Electrician would be called in to investigate. Still not an Immediate Danger though.
But in the general case, an install in good condition with a missing Earth, is potentially dangerous in the event of a Line to Exposed part fault, hence....C2.

You'd like to think so wouldn't you, but I went to a house a few months ago to do something or other and the lady mentioned that everyone felt a funny tingling when they touched a certain wall in the bathroom. I asked when this first happened and she said the day they moved in, which was about 13 years ago! (it was a cable in the wall with a capping nail touching live and after a shower the condensation made the wall damp enough to get a tingle)

There really is no helping those who can't help themselves
 
I would consider the lack of an earthing conductor to the MET to be immediately dangerous and hence a C1 (notwithstanding the fact that a fault would have to be present).
 
I would consider the lack of an earthing conductor to the MET to be immediately dangerous and hence a C1 (notwithstanding the fact that a fault would have to be present).

I can't knock you there because at the end of the day it's the inspector who decides what he thinks the code should be and he alone on his engineering assessment codes it, no-one else!. However all guidance on the matter to help the inspector decide points towards it being a C2 ....
 
I can't knock you there because at the end of the day it's the inspector who decides what he thinks the code should be and he alone on his engineering assessment codes it, no-one else!. However all guidance on the matter to help the inspector decide points towards it being a C2 ....

You're right!

That's it! From now on, no 30mA RCD for additional protection gets a C1 from me!
 
I can't knock you there because at the end of the day it's the inspector who decides what he thinks the code should be and he alone on his engineering assessment codes it, no-one else!. However all guidance on the matter to help the inspector decide points towards it being a C2 ....

You're right!

That's it! From now on, no 30mA RCD for additional protection gets a C1 from me!

True to an extent but this is clear cut c2

The easiest way to define between c1 and c2 to is basically can this situation cause harm right now exactly how it is.

No earth can't, it just has the potential to under fault conditions

So C2
 
Can you get a shock from it all else being well with the installation?

No?

Then it's not immediately dangerous is it!!!
I can't help playing devils advocate on this one.

Given the earth is functional as well as protective if the main earth is missing I'd say it would be reasonable to expect touch voltages of CPC to rise as electronic appliances are connected or even if there's an everyday surge or spike that causes surge arrestors to conduct. Neither of these events would be classed as faults so I could see the case for declaring it an immediate danger therefore I could see the case for declaring it a C1 issue.
 
Thats the beauty of an EICR, you as the inspector decides what you think the code should be based on your engineering assessment of the situation! If you live in a high 'surge' area, or have lots of electronics attached, or anything else that may introduce voltage onto the 'earth' then you may well declare it a C1 -- thats your engineering judgement!

If nothing of the sort exists then as a general rule C2 is recommended.
 
I think it 's not just 5WWs doing stuff like this - there are other factors. Firstly, as everyone knows , an eicr can bring in more work! There is still, and it's more prevalent in more technical trades, a (rightful!) distrust of sparks because people can make stuff up to get remedial work. Not sure how you can get round this one!!??

Secondly, there is a lot of hearsay - ppl taking stuff as read without thinking about it or looking at BGB. Eg - 12v light fittings/fans in bathrooms etc etc etc. I know I have been guilty of this but I am learning and am humble enough to be corrected.

But...solid education basis can definitely steer the 2nd kind of person - if it is drilled into them to question everything and how to use regs book well that helps too!

As for the cheating cowboys, I like to think that those blokes will never truly be successful and society and economics has a way of sorting wheat from chaff and honest from dishonest.

The only thing that can buck the trend is £millions spent on advertising, PR and marketing in the name of looking after people's world.

PREACH IT
 

Reply to EICR Code for no main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
684
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
32
Views
1K
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
460
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top