Doing a test the other day and found a couple of metal light switches no earth to faceplate just to back box but both lugs were fixed.
What code do you reckon I'm saying 3 but it's a 2 minute job anyway to rectify. Can't recall seeing it before though
Cheers
True but gotta find some faults for my money !
I find it's better to tell the customer there were a few very minor faults that have been rectified.
The faults you mention are not worth the time, effort and ink to note it down plus the time to open a what code debate on here
No code.. Aslong as there is one fixed lug no code required, faceplate cant be taken off until isolated, not to say i wouldnt tell the customer and refer to any manufacturers instruction.
Quote Bigspark "No code.. Aslong as there is one fixed lug no code required, faceplate cant be taken off until isolated, not to say i wouldnt tell the customer and refer to any manufacturers instruction."
How do you know a switch is safely isolated with out removing it from the box?
You dont without removing testing but how many metal clad consumer units,switch fuses grid switches etc use this method to earth the faceplate. Personaly I earth all metal switches with a flylead but its belt and braces.
Most manufacturers instructions recomend "earthing"
bollox. the faceplate must be earthed. a fly lead to the box is optional.
Im not saying i wouldnt put a fly earth lead to it as i 100% would but to fail this on a eicr you must put a reg no aggainst it.! Exacly db covers grid faceplates are good examples
Neither of which ususally have any live terminals on them, therefore becoming just a piece of metal once removed. Unlike the switch which the OP asked about.
As I understand it, the back box does not require a fly-lead if the back box has a fixed lug. My preference is to fit one anyway.
However, the faceplate/grid yolk should be earthed - you cant rely on the fixed lug to earth the switch assembly from the back box via the fixing screw.
You seem to contradict yourself there. We are not talking about prefrences im sure all members on hete would earth it but were talking eicr coding which need to ref facts and regs
Reply to Eicr coding in the UK Electrical Forum area at ElectriciansForums.net
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Deleted member 155212
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...