Putting on my student's tin hat, I'll give it a bash :

For bonding we are concerned about touch voltages and so the path must be comparable to the resistance of Cu and so we use resistivity ratios (>8). For use as CPC we use the adiabatic eqn and its k factors that include temp rise and thermal capacity of the materials. This gives a reduced steel requirement compared with bonding calcs and so SWA armour is often ok for CPC but not for bonding.
 
So by calculation you would need a 70mm 4 core to get the equivalent of 16mmcpc. How come we see so many sub mains being ran with the steel being the cpc if it doesn't comply?

Because CPC size is calculated by the adiabatic equation and not by the equivalent conductivity method used for bonding. the CPC only has t carry fault current for a specified time which is limited by the fault protection device and so can be a lot smaller than the bonding conductor required on TNCS.
 
Sorry, a combination of me not following the thread correctly, reading it in my phone with a cracked screen and getting completely mixed up. Cpc is correct and won't need to be altered. As for the bonding it's not man enough so a recommendation will need to be put down
 
Pete that's a link to the pdf copy in a folder on your PC desktop. So hopefully inaccessible to the outside world.
And I suspect admins will not allow a copy on the forum of any of its content due to copyright.
 
Pete that's a link to the pdf copy in a folder on your PC desktop. So hopefully inaccessible to the outside world.
And I suspect admins will not allow a copy on the forum of any of its content due to copyright.
Oh sorry I thought I had posted a copy of the chart, can admin please delete
There is a comparison chart in the OSG
file:///C:/Users/Pete/Desktop/Electrical%202/SWA%20CPC.pdf
Admin can you please delete my reply
 

Reply to EICR question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...
Replies
8
Views
414
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
845
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock