joehat
Hi all
Done an EICR today and on one light circuit my zs tests was coming with error so got the 2 poor tester out, and I'm getting 50v between 230 l-n and 50v l-e
Checked all switches and light fittings Ect, nothing obvious, property 13 years old,
I've checked all downstairs and seems to be near the cu as same readings on all, so gonna find out when next their which one the 1st light is, and then test the earth after that to the other lights and I then I'll know more where the issue is.
Would you say this is either a poor connection hidden somewhere or a screw through a cable Ect , any ideas.