Discuss Eicr in the UK Electrical Forum area at ElectriciansForums.net
Davem
Right guys first EICR found some C1&C2 codes obviously once thee have been rectified what certification do you give the client once a satisfactory ??
Thanks Trev with regards t that, I have a hob plug in a socket, shower on a to small of a breaker, no blanks in consumer unit etc. how would I go about filling the minor works cert in. I ask because I'm not really changing the wiring I'm just rectifying the problems, would there be a need a test again if I'm simply changing a breaker ?? Thanks again Trev
Davem why are you asking about Eicr's when it say's on your profile that you are a factory worker, am I missing something ??
Yeah sorry lads need to update profile was a factory worker put myself through college, and passed elecsa part p in March
A hob on a 13 amp supply is unlikely to work, what is the wattage of this hob? If it's low enough to be on a plug top why are you pulling it?
Shower on wrongly rated MCB, what is the wattage of the shower and MCB?
No blanks in a CU, send the customer an invoice detailing the blanks supplied and fitted.
If you're changing an MCB you are potentially changing the circuit characteristics and this would require a installation cert (imho) and yes, for that reason you would fully test the circuit to ensure it still complies. However, if it is a like for like replacement there is an argument for no cert required but I'd do one just to cover my backside if nothing else.
A covering letter always gets sent with any remedial works I carry out mate. As you can't exactly write a test form for fitting blanks into a db! Hope this helps
Shower is 10.5kw fitted with 10mm cable on 40amp mcb, for the hob it's supplied from a 32amp breaker in 6mm junction box to a double socket hob and oven plug in.
I don't like the sound of the junction box, should be on an outlet. Assuming the wattage is ok for a 32 amp supply then there's nothing wrong there and if the oven is less than 2KW then the recommendation for a dedicated supply doesn't apply.
Don't think either of those things warrant a C1 or 2 though mate
Oven is fine on a plug it's just the hob I'm a bit worried about, completing tomorrow so will doubly check this. What's your thoughts regarding the shower Trev ?
so..
how many KW is the shower?
and why do you think the MCB`s I N is too low?
what is the CSA of the shower cable?
edit: sorry about that...just seen a post with the info on it..
so...
you know that MCB will hold for upto 1.45 X its I N for upto an hour before it lets go dont you...
whats the installation method of the shower cable?
so...
Still should be on a 45 anyway. Not good practice to leave it running over its rating. Daz
i'd be getting a clamp meter on that shower before condemning the 40A MCB. be very surprised to get >40A even on a good day.
Reply to Eicr in the UK Electrical Forum area at ElectriciansForums.net
Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
I was surfing through one of the electrical training groups on Facebook yesterday and came across this question from an AM2 prep course: There...
HI , potential 2 bed 1970’s bungalow buyer here…. Our surveyor (RICS) has pointed out there is no circuit breaker to the electrics (fuse board...
Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Hi all, Been asked to do EICR on thatched property for insurance purposes, however they will want all C3 codes rectified. Haven't seen it yet but...