As there are so many “different ways to skin a cat” in our industry, I thought I would post the below to see if anyone has anything they would like to share on a job I have coming up


60m2 ish of electric under floor heating split into 3 zones and also on 3 stats (stats can only switch a max of 16a unless you install contactors etc) zone 1 is kitchen, Zone 2 is hallway and zone 3 is bathroom total loading around 9kw / 37a


I am thinking it’s probably best to run a separate radial for both kitchen and hallway from the CU given the fact these are the largest areas and can probably only fit 2.5mm into back of stats etc and then probably pinch a feed from the ring via an FCU for the bathroom


Like I said, there are many different ways to do it but just thought I’d throw up a post whilst I was online. Haven’t really given the job much thought as yet.


Cheers
 
and don't forget to bypass the meter. :38:
 
  • Like
Reactions: 5 people
Continuous loads over 2kW (such as UFH) are recommended to be be on their own circuit's.
Depending on the bathroom load it may need it's own circuit, but also ensure it has an earth screen and 30mA RCD protection.
 
Continuous loads over 2kW (such as UFH) are recommended to be be on their own circuit's.
Depending on the bathroom load it may need it's own circuit, but also ensure it has an earth screen and 30mA RCD protection.

Own circuit seems a better idea to me yes. Earth screen if needed with the type of UFH fitted. Daz
 
Also,depending what stats you select,check the type and maximum load they are suitable for. Some state 16A,but this is a maximum,and in my experience,certain types fail prematurely,when operating near their upper limits.
 
Thanks guys.. makes sense and good advice. seems like I was pretty much there anyway, just wanted to make sure. cheers
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
electric ufh install
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
lews123,
Last reply from
lews123,
Replies
5
Views
1,634

Advert