Hello there.
I have been asked to look at a new supply, 240 volt to a stable block. Problem being is distance likely to be between 150-175 metres. Volt drop gonna be a problem. DNO quoted £30k to run new cable from sub. The stable block includes a kitchen, toilets, office so they were looking at a 80/100 amp supply! This is a bit out of my comfort zone so some advice would be helpful. The customer, to cut down costs will dig trench and lay cable themselves.
Many thanks.
 
You just need to do your calcs and select the correct cable for the volt drop. You need to work out the design current it wont be 80/100amp for that you would be looking at 70 or 95mm and a few thousand pounds. Get the design current then you can work out the volt drop. The cable wont be cheap but that's how much it's going to cost them. It will be cheaper than 30k though!

Use SWA buried with warning tape above it. Deep enough as to prevent danger. Is it a farm?

Sent from my Xperia S using next doors WIFI
 
Be careful to check the system as well as its out in the sticks it may well be a TT in which case you'll need RCD protection.
 
Hello there.
I have been asked to look at a new supply, 240 volt to a stable block. Problem being is distance likely to be between 150-175 metres. Volt drop gonna be a problem. DNO quoted £30k to run new cable from sub. The stable block includes a kitchen, toilets, office so they were looking at a 80/100 amp supply! This is a bit out of my comfort zone so some advice would be helpful. The customer, to cut down costs will dig trench and lay cable themselves.
Many thanks.

After you have scared yourself silly, trying to find a single multi cored cable to suit your requirements, Think about the use of a smaller sized parallel cabled sub-main. You may well be pleasantly surprised!!! lol!! ...Just make sure, that whatever way you decide to supply this stable block ensure that the cable trench floor is free of sharp stones and debris etc, and lined with a suitable depth of soft sand on which to lay your cable(s). And it should be the cables covering medium also. Don't forget to conduct a sheath test on the cable(s) prior to the final backfill layer....
 
After you have scared yourself silly, trying to find a single multi cored cable to suit your requirements, Think about the use of a smaller sized parallel cabled sub-main. You may well be pleasantly surprised!!! lol!! ...Just make sure, that whatever way you decide to supply this stable block ensure that the cable trench floor is free of sharp stones and debris etc, and lined with a suitable depth of soft sand on which to lay your cable(s). And it should be the cables covering medium also. Don't forget to conduct a sheath test on the cable(s) prior to the final backfill layer....

As Engineer54 Say's , parallel is the way forward ! We have just laid 400m of 70mm 4c to a small barn conversion come holiday home on Wednesday , instead of a substantially larger 2 core .

Also he mentions the importance of the bedding and back fill material , I can unequivocally support that statement due to a length of 340m 95mm 4c we are about to replace next week under warranty !

Some may remember me mentioning a issue with this sub a few months ago and the need for some fault location equipment , well let's just say multiple fault's would not even cover the first couple of meters let alone the rest of the run !!!!!!!

Just to note though ! We did not lay it in the first place and did not even supply it , but as most things in life " it's complicated ! "
 
As Engineer54 Say's , parallel is the way forward ! We have just laid 400m of 70mm 4c to a small barn conversion come holiday home on Wednesday , instead of a substantially larger 2 core .

Also he mentions the importance of the bedding and back fill material , I can unequivocally support that statement due to a length of 340m 95mm 4c we are about to replace next week under warranty !

Some may remember me mentioning a issue with this sub a few months ago and the need for some fault location equipment , well let's just say multiple fault's would not even cover the first couple of meters let alone the rest of the run !!!!!!!

Just to note though ! We did not lay it in the first place and did not even supply it , but as most things in life " it's complicated ! "

Remember the thread. You’re having to replace under warranty when the customer installed the cable? That’s a bit harsh!
 
Not the half of it Tony !

I do not want to go into it on a open forum so may pm you with a explanation latter if i have time to type it ( exceptionally slow typist !) , but we have essentially taken the hit as a matter of honour !
 

Reply to Electrical supplies over long distance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Electric Car Charging at Home - Comprehensive Guide As EV ownership and the transition towards electric cars rise, having a home...
Replies
0
Views
109
I want to run power to an endpoint about 600 metres away to power some security cameras and some power points. I'll be using a qualified...
Replies
16
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'm converting my old garage into a two bedroom annex. At its nearest point it is approx 10m from main house. I plan it to be all electric, UFH...
Replies
5
Views
3K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
790

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock