Reg. 701.411.3.3 RCD for bathroom circuits. Suppose 4 12v downlights in bathroom ceiling, trannies in loft, switch outside bathroom. As there is no 230v in bathroom, does the aforesaid reg. apply? Max. touch voltage well below 50v. Other opinions sought
 
yes all circuits in a special location ie, bathrooms are to be protected by means of a 30 mA rcd or rcbo,17th edition is retraspective by that i mean that if you are adding a new circiut to an older installation then you have to take into consideration how old the existing wiring is , as not all buildings are to 17th edition.. but all new wiring is to be installed to bs7671 , 17th edition,
 
not a new circuit, just light replacement. no RCD on installation. ideally RCBO on lighting, but my argument is that there is no " mains" in the bathroom. only 12v.
 
i don't think the reg does apply then teletrix , as even if there was 230 to lights they are out of zones and if the appropriate ip ratings are correct you should be ok..
 
that's what i thought, but would like other views. btw, you missed the c in my name, lol.
 
This reg is included in the Q&A forum on the ESC website,
Is Regulation 701.411.3.3, which requires RCD protection for all circuits of a bathroom or shower room, intended to apply to ELV circuits?
No. This is intended to be clarified in the 17th Edition in due course. However, RCD protection would be required for the circuits supplying ELV sources (such as transformers) if those sources are in a bathroom or shower room.
17th Edition Guidance | New or Rewired Domestic and Similar Installations
 
Last edited:

Reply to ELV in bathroom in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I live in a property built in 1911. It has had asbestos artex applied to every ceiling in the house. I am currently creating a new...
Replies
1
Views
2K
Hi all, I'm refitting my bathroom in my first floor flat (top floor) built around 1989. It has 2 CUs, one for night storage and one for 24h...
Replies
39
Views
4K
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet...
Replies
31
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all! This is my first post and I have registered to ask for some help with troubleshooting an electric shock I got from a plastic light switch...
Replies
44
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock