Discuss EV charging point query in the Electric Vehicles Advice Forum area at ElectriciansForums.net
Andy C
I have a nice job on in a few weeks which includes wiring up a solo chargepoint EV point. The pod doesn’t have its own RCD like Rolec do.
I am rewiring the house and intended to use either a type A RCD or RCBO.
As they also detect small levels of DC leakage.
I use BG consumer units but I don’t think they do them.
What are the views of changing one of the general type AC RCDs for another type A make or do I go for a whole new board.
Thanks in advance.
The manufacturer suggests using a type B RCD.
It may be best to install a separate enclosure with a type B RCD to protect the EV point.
To install a different manufacturers RCD in a BG board is not really ideal and definitely more prevalent in the current regs as a non permitted option.
The manufacturers installation instructions are 2017 and out of date, they apparently quote regs that don’t exist. They suggested that the pod,point could be fitted using the TNCS system. Whereas I understood it had to be a TT Island in this case.
I will probably go for a different board as I wanted to keep the board neat with the circuit supply in the dB.
The Rolec stuff looks much better but the client has already bought the charge pod.
The best source of rcds or rcbos for ev chargers is rolec. They are between 15 and 20 quid depending which wholesaler you go to. Give them a call and they will give you the product code to use in the wholesalers.
Can put one in an enclosure adjacent to cu to supply the charger fed via a unprotected mcb. Not familiar with chargepoint as i only install rolec or evbox. Both have integrated protection.
Out of interest what mcb do they recommend for the chargepoint units?
Some makes recommend type c over type b.
Thanks in advance.
Hi there
In the new wiring regs you can’t swap and change the breakers or RCD with different makes unless you become the “manufacturer “ and can certify them as fit for purpose as mixed suppliers.
You will have to buy a full board by another manufacturer with type A installed such as Hager do as standard now or install a separate board with main switch and an rcbo
Reply to EV charging point query in the Electric Vehicles Advice Forum area at ElectriciansForums.net
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Electrical2Go - Green2go Launches for All Your Solar, EV Charging and Renewable Needs Green2Go - for All Your Solar, EV Charging and Renewable...
Just taken deilvery of an Electric Car (Mini Electric) and so doing some research into installing a charge point. Supply is a standard Single...
4K