Working on supplying three phase power to a new shed in a farmyard. Running armoured underground. I was going to connect the armour to the earth rod at the Main DB then use the armour at the other end in the new shed as the earth in the new shed, bonding all extraneous metalwork to it. Is this acceptable or do I have to use insulating gland at new shed end and new earth rod there? Some confusion, as all existing outlying building have no earth rods of their own, just rely on cable armour back to main earth rod.
as steve said. rod it at both ends. the more rods the better. bit of luck , if you use 5/8 screwed together rods, go deep, you might even make engineer54 happy.
he can have mine now. i've no further use for him.
Ha ha!! .... Just the use of ''Real'' earth rods will make me happy!! lol!!
Preferably, at least 2 of your 1.2 m rods coupled together for depth and stability. As for how deep i normally go down, ...well i haven't used anything other than 3.2m, 3/4'' rods for as far back as i can remember now, so i guess that would be the depth i'm happiest with...lol!!
Reply to Exporting Earth on TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...