Talk nicely to the next passing electric board man you see, the local SEC guys have them as standard van stock items and are happy to give handfuls away if you engage them in a bit of banter.
(same trick applies to the BT gel crimps if you see someone working in a telephone exchange box)
 
  • Like
Reactions: pc1966
Donning some PPE before doing so of course.
 
Find a 'short' offcut of 25mm tail, form it into a U shape and install one end in each of the two vacant holes. 😀
yeh... ok.... ive got an unused hole in the live and neutral blocks.... Will this still work?😳⚡💔
 
Hence the inverted commas around 'short'

Donning some PPE before doing so of course.

I wasn't suggesting doing it live. You might want to re-close the isolator with a gloved hand though.
 
Last edited by a moderator:
  • Like
Reactions: pc1966
A thin plastic shim can sometimes be inserted between the brass block and the casing of the Henley block
That’s why we use the Ashley blocks as they come as standard with the little shims. Always have spares in my tool bag.
 
Well had a look yesterday and in fact the blocks are Proteus ones, presumably installed by the smart meter folks as they have seals on them (for no obvious reason, given they are on the consumer's side):
meter-and-tails.jpg
Just now I am not sure if I should disconnect the old storage heater tails, it might be more hassle than it is worth. As an interim measure I removed the fuse wire from the 3 * 15A rewirable fuses in the dedicated CU (presumably it used to have a white-rate meter and time switch) so if anyone switches it on to see what happens then nothing will. I doubt those circuits have been tested/inspected since the heaters were removed a decade or two ago.

Will see if I can pick up any Proteus blocks for the blanks as some point.

I don't like the 16mm T&E arrangement either, but that is even more hassle to deal with!
 
Last edited:
Will see if I can pick up any Proteus blocks for the blanks as some point.
If you can’t get any, I’ve got a couple in the van if you want me to post them up.

Just the blanks…. Not the whole blocks
 
  • Like
  • Friendly
Reactions: pc1966 and DPG
If you can’t get any, I’ve got a couple in the van if you want me to post them up.

Just the blanks…. Not the whole blocks
Thanks for the offer - finally I can send a "stamped addressed envelope" like in the old days!
 
  • Like
Reactions: DPG
Also to add, the taper around the DNO fuse is apparently due to the seal hole, etc, being damaged. Though the smart meter install took place after then (or maybe caused it?). Again, not something I'm inclined to monkey with.

I don't know what the green metal box at the bottom is (one white cable exiting sideways, two black cables exiting downwards) either. I suspect it might be some sort of outdoor thermostat that was part of heating control, but if anyone recognises it can you let us all know?
 
the box down the bottom.... it looks like some sort of sounder.... the two holes have buzzers underneath?
No idea if that's right.... just brain chatter
 
the box down the bottom.... it looks like some sort of sounder.... the two holes have buzzers underneath?
No idea if that's right.... just brain chatter
Next time I am there I can investigate with a voltage tester at least to see if it is still live, etc.

I suspect many properties end up with odd remnants of past installations. What is odd about that is it being out in the meter cabinet, it has no obvious controls which is why I wondered if it was a thermostat or similar.
 
Plus 1 for weatherproof compound.
It fits in very snuggly.
 
What's wrong with a tube of decent RTV silicone, such as this:

It has the advantages of fitting any shape/size of hole.
I expect some of the cheaper tubes/cartridges will work as well, though better to get one rated for electrical use.
 
Surely that tube would not fit in a Henley Block? 🤣

Still think the best idea is a Golf T.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

pc1966

Esteemed
Arms
Supporter
Joined
Location
Dundee
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Fill unused holes in Henley block
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
pc1966,
Last reply from
Mike Johnson,
Replies
36
Views
11,158

Advert