Just finished installing some low voltage downlights to an existing circuit , I'm going to test tomorrow to save disconnecting the lamps/transformers I was going to test LN-E 500v on the insulation resistance test , what do I have to write on the minor works certificate and where to show that ive done this? do I have to include anything in the departures section? And on the Live - Live IR Test section do I just write N/A? Thanks
 
Where it's impractical to test between L-L, I write N/V as you have not verified that particular test.
 
I generally write beside the insulation resistance LN-E only.
 
Agree this as a limitation with the customer pre test.. Then in insulation rersistance box L-L put Lim.
 