As has been stated it isn't necessary to do a complete set of tests on an unmodified ring final circuit. End-to-end should be adequate if this doesn't bring up any problems (perhaps at a socket outlet rather than dis board - controversial I know but much handier). Unnecessary dismantling is as likely to introduce faults as find them.
 
Interesting little thread this, all of the answeres are spot and, but amazingly there are differences to them, just shows you in this trade.

I'm guessing in the UK that 80% of socket circuits are ring finals, and I have often wonder why we still persist in them. They were designed and really inclusively developed for the UK. After the war shortage of conductor material was the mother of invention.

But now loads have altered, we rarely use heaters plugged into a socket now with central heating, and apart from a kettle and an iron there is very few heavy loads that isn't on a dedicated circuit as per appendix 15.

I'm amazed that there is not more use of a 2.5mm 20amp radial circuit taught in the UK. Ease on installation, and ease of testing must be worth the thought alone.

I'm not decrying the ring final/main, often there are good design reasons for it, external lighting in car parks springs to mind. But for BS 1363 sockets, is it out dated?
 
Last edited:

Reply to Final Ring Test during EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
839
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock