Hi guys

Im new here im currently in my first year on elec installation at college yale in wrexham to be precise.

Im wanting to wire 2 500watt floodlights but they need to be portable so i want them on a normal 13amp plug top. So I will obviously need to use flex so am i right in thinking that i need 1.5mm2 flex?? also what size fuse will i need to install in the plug top. Asuming it is ok to wire 2 500 watt lights like this i cant see why but im no expert.

Thanks Ashley still learning.
 
2 x 500watts = 1000 watts / 230V = 4.34A 5A fuse will do.

Flexible 1.5mm cable rated at 16amps.

Where are they to be used?

These lights can get very hot and heat resistance cable maybe more suitable?
 
Basically i race radio control cars so everyweek we rent a hall. But last week the hall was rewired with new lights but the new lights are in diffrent possitions to the old ones. So they dont light up our pitting area as well, so we asked if we could wire in a couple of flood lights they said no. So we asked them if we could put the lights up but not be hard wired in, just have them on a socket and then take them down each week they said yes aslong as it is safe and done properly.

A
 
I would like them on one plug top but if that just isnt possible then it might have to be two. I asume it would be ok to wire 2x 250 off one plug top?

A
 
I would like them on one plug top but if that just isnt possible then it might have to be two. I asume it would be ok to wire 2x 250 off one plug top?

A

Never good practise to wire more than one appliance off of one plug top.

Use your P=VI equation to work out your current drawn, it will be good practise for college.
 
I got the idea from a portable teloscopic flood light we have sort of thign you might have on a site that has 2 on one socket is there any sort of junction box i can use to connect two units to one socket. I just dont want to use to many sockets up in the hall.

A
 

Reply to Flood lights in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

A
the situation is this: 8 x 24v rgbw flood lights for a garden, each fitting has power consumption of 45w. 3 lights into a 200w driver, another 3...
Replies
4
Views
486
Hi.. Newby here.. I have a couple lights holders/bulbs on the end of a flex plugged into the mains 13Amp plug. I want to put an inline switch on...
Replies
3
Views
701
For the bathroom, want them matching and one needs to go over the shower. Also need to be ok with insulation over the top. Ideally fit in the...
Replies
2
Views
219
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
2K
As the title says. But then I cut off a jst connection off one of the light strips and I can't get them to work together... the one strip is plug...
Replies
1
Views
551

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock