As an apprentice I was given scrap ends to make off, After a while and some intense inspections of my efforts I was allowed to use potting compound. The first end I made off that actually went into service made me a very proud puppy spark.
Afaik it's still there to this day.

your gran kids might get the chance to rip it out while complaining its better than what they are replacing it with you never know
 
Well so far we're one from three and it looks like it's staying that way. Grandson will not be a spark if I've got anything to do with it.
 
No point in testing until you have potted the gland......this will be another learning curve, testing the insulation with one reading..then testing 24 hours later, with another reading. Full marks, for taking the time to practice and post your results. In the next few years, when industrial projects need installing and renewing...The quick course guys will be left to their house bashing, whilst others will be back in the thick of it.
 
A decent effort.
when doing it for real remember and put the compound in from one side only of the pot.
keep the compound clean and free from bits of swarf etc.
i wouldn't blow in the pot as mdj suggests I would give it a tap and make sure it's clean myself
like all black arts practice is the key
 
Blowing in the pot is potentially bad news. You could have bits of swarf in there which could blow up into your eyes.
Tappy tappy is much better.
 
Blowing in the pot is potentially bad news. You could have bits of swarf in there which could blow up into your eyes.
Tappy tappy is much better.

to be honest I didnt blow into it, I wiped conductors first to get rid of most of it then tap.

I didnt touch compound either, I used the wrapper and overfilled it from one side to stop the formation of any air pockets
 
Beware of a tiny thread of brass/copper swarf which can sometimes appear in the pot as you screw it onto the cable.

Also pop the megger on it before you put the compound in, and then just before you crimp it, and then after you crimp it. this was you have a chance to correct things before you crimp it and get to the point of no return.
 
Shanky...are you using a cutting compound or oil when cutting....if you find this messy, old trick from an old sod...is use a candle, just as good, less mess and saves you joist blade
 
Joist blades, ware very quickly, if you use oil, wax or compound anything is fine...but nothing will result is 3-4 cuts, then some really bad snagging and a lot of swearing.
 
The reason you shouldn't blow dust etc out of a pot is because your breath contains moisture which will lower the IR test, obviously.
The moisture will never dry out after the seal is fitted, because it cannot escape.
 
Joist blades, ware very quickly, if you use oil, wax or compound anything is fine...but nothing will result is 3-4 cuts, then some really bad snagging and a lot of swearing.

Use a T bar, then, and a ringing tool....not an alarm for when you've stripped the right amount, by the way
 
The reason you shouldn't blow dust etc out of a pot is because your breath contains moisture which will lower the IR test, obviously.
The moisture will never dry out after the seal is fitted, because it cannot escape.

You're going to blow on it (if you're daft enough) for a second or two, this will not give the insulant much moisture at all, any moisture it absorbs will disipate almost immediately.
How much residual moisture is in the air around us at any given time?
 
The reason you shouldn't blow dust etc out of a pot is because your breath contains moisture which will lower the IR test, obviously.
The moisture will never dry out after the seal is fitted, because it cannot escape.

Minor problem, done thousands with a short, sharp blow. Never straight after a brew, though :drool5:
 
You're going to blow on it (if you're daft enough) for a second or two, this will not give the insulant much moisture at all, any moisture it absorbs will disipate almost immediately.
How much residual moisture is in the air around us at any given time?
Quite a bit, try it.
 
The point is that as soon as you've stripped, the insulant is going to be absorbing moisture from the atmosphere. The tiny little bit from a short sharp blow is irrelevant.
I never blow on it but for a different reason

Understandable.
 
The reason you shouldn't blow dust etc out of a pot is because your breath contains moisture which will lower the IR test, obviously.
The moisture will never dry out after the seal is fitted, because it cannot escape.
So what would you think the main content of potting compound is made of (oil & water perhaps), this is why ir readings are all over the place, until it drys out....!!
 
So what would you think the main content of potting compound is made of (oil & water perhaps), this is why ir readings are all over the place, until it drys out....!!
It doesn't dry out, it cures. It certainly isn't made from water. Once sealed, how would it dry out, how many bottles of unopened water do you see drying out?
Its not like breathing on a mirror where the condensation dries almost immediately, the magnesium powder soaks up any such condensation and would be held there by said compound - as small as it may be. In my book, blowing into a pot is just a no go when making off micc ends.
 
I am not lying if I say I have terminated thousands of ends, seriously thousands, and I blow the dust out of everyone, I rewired a childrens home 20 years ago in pyro and it is still working fine today lol
 
It doesn't dry out, it cures. It certainly isn't made from water. Once sealed, how would it dry out, how many bottles of unopened water do you see drying out?
Its not like breathing on a mirror where the condensation dries almost immediately, the magnesium powder soaks up any such condensation and would be held there by said compound - as small as it may be. In my book, blowing into a pot is just a no go when making off micc ends.

Never heard anything so ridiculous for a long time.....

If your hypothesis were correct, literary every pot ever made off, is sealing moisture into the cable from the time of termination.... Just how hydroscopic do you think the magnesium power is for gods sake?? Are you one of these people that think left unsealed for any amount of time, moisture will penetrate the the whole coil?? I'll give you a clue, it took years (around 6 years to be exact) for moisture to travel a couple of foot in a coil of MICC cable that got left at the end of the garden, semi open to the elements.

Some tap and some blow any mag dust or copper filings out of a pot prior to sealing, one things for sure blowing isn't going to matter one jot, and you can take that to the bank!!
 
pyro was changed slightly in the early 80's I believe before this the filler was just a powder and it was common to have to leave about 2 foot spare for a termination especially outside as it did absorb moisture reasonably readily,however when it was modified a moisture repellant was added to the mag powder and it absorbed even less moisture,I think iirc that it was quoted as somewhere along the lines of less than 1 inch per week for open pyro in a damp environment and even then the application of a little gentle heat from a gas torch would soon dry this out,I think most of us that have worked with the stuff have blown out pots and not seen any problems.For me the most common cause of failure that I saw was the conductors touching within the pot,the best way to prevent this is careful alignment of the pot and seal and then after crimping to give a gentle pull on the conductors as this will ensure they have not been moved during crimping.
 
We were using MICC 240mm singles (Trefoil & N) with ultra high temp seals to supply the emergency power supply side of metro stationS (MTR) switchboards in Hong Kong. The humidity present underground during construction was almost unbearable. Like you would be working in a pair of shorts a hard hat and boots and that's it!! Sweat pouring off everyone, ....To my knowledge, not once did a problem arise from moisture entering the MICC cable during the termination processes, the tails of these cables all being in the region of around 600 to 800mm or thereabouts...
 
I can only say I am a little surprised by the differing opinions. As said in my first post (#58) this is how I was taught, starting in the trade in 1972. Some things stick and this is one of them. Maybe phil d in post 78 has hit upon something that my early teachings stem from, who knows? Maybe its over the top twaddle?
I do admit to having a few blows myself in the past (strictly MICC you understand - nothing perverse), but not often and whether correct or twaddle I would still say it is good practice not to.
I don't think I suggested that the mineral insulation was anywhere near as absorbent as lets say talcum powder - as is isn't, but as said all down to good practice, and am a little surprised that E54 doesn't support that.
Either way, its not important, I haven't made an end off for a good 20 years or so now, but in my early days made them off in abundance. Should I come across an MICC installation before I retire, I shall try and refrain from blowing :)
 
Last edited:
but as said all down to good practice, and am a little surprised that E54 doesn't support that.

I would support any good practice that held creedence, unfortunately refraining from blowing out a MICC pot prior to sealing doesn't hold any credence for me. As i say it doesn't make one jot of difference...
 
You probably saw one of my first attempts Trev!! Got a right ear-bashing for it... no shroud, pot not straight and screwed on to far...

btw - I've a spare one of these if MDJ can't set you up...

Edit - didn't realize the pic was that big, i'ts only for 20mm pots :)

thanks for the offer of a spare potting tool guys, the local wholesaler's are very good and he has managed to get me one at a reasonable price.

£35 inc vat etc.

not bad considering I only spoke to him about it tuesday after 5pm
 
got my potting tool today so gave it another go

ga2a3y7y.jpg


yqy9erah.jpg


4aseja7e.jpg
 
Take it to work and IR it mate, just out of interest.

I did take the other one to work and did ir it, got about 60Mohm.

to be honest I didnt cut any off coil or try to get any moisture out of it first before I made end of so who knows.

this one should have a lot higher reading?

it was a little odd because it fluctuated from 50mohm to > 299 at 500v. im guessing batteries in tester could be low because didnt get constant reading
 
I did take the other one to work and did ir it, got about 60Mohm.

to be honest I didnt cut any off coil or try to get any moisture out of it first before I made end of so who knows.

this one should have a lot higher reading?

it was a little odd because it fluctuated from 50mohm to > 299 at 500v. im guessing batteries in tester could be low because didnt get constant reading

or there may be a slight bit of moisture there and the IR test is drying it out, thus readings will rise as you keep the tester on it.
 
quote_icon.png
Originally Posted by shanky887614
I did take the other one to work and did ir it, got about 60Mohm.

to be honest I didnt cut any off coil or try to get any moisture out of it first before I made end of so who knows.

this one should have a lot higher reading?

it was a little odd because it fluctuated from 50mohm to > 299 at 500v. im guessing batteries in tester could be low because didnt get constant reading


or there may be a slight bit of moisture there and the IR test is drying it out, thus readings will rise as you keep the tester on it.

The correct method of IR testing a new circuit/build is by applying the test voltage for a minimum of 1 minute... Most electricians, will if you're lucky IR test for 10 to 20 seconds. lol!!
 
Tut. tut!! They don't seem to be teaching much at all at college these days....

they only teach the questions/answers that are in the exam now, only reason I didnt need any resists in final year was I studied off my own back online.

everyone else needed a resist or really struggled.

one question in jtl test was how deep is recommended for a bore hole for the average sized house.

no mention in revision books etc that we were supplied with etc and even tutors were clueless when I mentioned it after exam
 
thought a bore hole was where you put the father-in-law when you couldn't take any more of his verbal diorrhea.
 

Reply to FP Cable Is Not Always Suitable in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I was tracing some electrical cabling last night and noticed a ~6" section of 2.5 T&E cable that appears to have been subject to heat damage and...
Replies
19
Views
2K
Hello all I'm doing a Job in France for my company where we are installing SWA for power to our own control panels The issue is the DB is a...
Replies
46
Views
9K
Silly Sausage
S
I have a goods lift where I work which is being overhauled, part of which will involve some rewiring of the control circuits to upgrade the...
Replies
9
Views
2K
I'm a Facilities Manager and not an electrician though I do have some electrical qualifications of some years ago. I wonder if anyone would like...
Replies
4
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock